A: Yes. I used 4/0 AL cable on both the main lugs and the feed thru lugs. Just make sure the panel is well anchored because you will be doing a lot of bending and tugging when routing the cable.
by|Aug 21, 2020
2 found this answer helpful
A: Yes.
by|Feb 19, 2019
A: Yes, the 200A main breaker is good for up to 250kcmil. See attached excerpt from the datasheet.
by|Dec 20, 2022
3 found this answer helpful
A: Thank you for your question. Yes, the TM820RCUFLP wire range is from #1AWG -250kcmil (Cu), and 2/0AWG -250kcmil (Al).
by|Jan 15, 2021
3 found this answer helpful
Q:Can the main be replaced with a 150 main?
by|Dec 12, 2018
2 Answers
Answer This Question
A: Thank you for your question. This load center is rated for 100a. The main cannot be replaced with a 150a main. I would suggest a TM1615RCU, TM2415RCU, or a TM3215R64K for a 150a outdoor main breaker.
by|Dec 13, 2018
A: I don't believe the busing is rated at 150 amps
by|Dec 27, 2018
Q:What type of breakers compatible with this panel? do you have the Part # on for for 20Amps 2 Pole, 30A-2Pole alos for main 100A-@pole?
by|Oct 15, 2018
3 Answers
Answer This Question
A: Square D homeline breaker’s work in this panel. The model number for the 20 amp double pole breaker is HOM 220 CP
by|Dec 16, 2018
1 found this answer helpful
A: I used GE breakers. Do not recall part #s
by|Dec 16, 2018
1 found this answer helpful
A: This panel uses THQL style breakers only. 2pole 20a would be THQL2120 and 2pole 30a would be THQL2130. A 100a main in already installed.
Thank you for your question.
by|Dec 16, 2018
1 found this answer helpful
Q:Whats the largest in wire this box can handle. Thank you
by|Aug 14, 2018
1 Answer
Answer This Question
A: #1-250 CU or 2/0 - 250 AL
by|May 5, 2023
Q:Can the factory installed 100 amp main be replaced in the field with a 60 amp main breaker for reduced load applications?
by|Jun 13, 2018
2 Answers
Answer This Question
A: Yes as long as the 60 amp will fit . Normally if your using this panel as a sub you do not need a main. As this panel would be run off 60 amp breaker in the main panel
by|May 5, 2023
A: Yes as long as the 60 amp will fit
by|May 5, 2023
Q:the size of the panel
by|Apr 28, 2018
4 Answers
Answer This Question
A: 5 1/4 deep, 29 tall, 13 wide. Mind is a pole mount on exterior plywood
by|May 5, 2023
A: The size is:
Load center depth (in.)
4.625
Load center height (in.)
28.6875
Load center width (in.)
12.5
by|May 5, 2023
A: Dimensions
Load center depth (in.) 4.625
Load center height (in.) 28.6875
Load center width (in.) 12.5
by|May 5, 2023
A: Approximately 14" x 30"
by|May 5, 2023
Q:I need 16 spaces but I have only 12 in my breaker box. Do I have to change the whole box or can I just change the inside panel?
by|Feb 28, 2018
3 Answers
Answer This Question
A: Hello Russ. I’m Chris from the Home Depot’s how-to Community. Thank you for your question.
Yes, you have to change out the entire box.
I hope this helps,
Chris.
.
by|Mar 12, 2020
A: 4 piggy back breakers will use 4 spaces but allow overcurrent protection on 8 circuits that would leave 8 single pole slots.
by|May 5, 2023
A: Howdy Russ,
This box is not able to be reconfigured.
You will need to add a breaker box with more receptacles.
happy fixing,
Coach Dave
by|Mar 12, 2020
Q:Can this be installed with main breaker at the bottom? The wiring to feed this panel is coming from the ground
by|Jan 23, 2018
2 Answers
Answer This Question
A: No
by|Dec 27, 2018
A: No
by|Oct 17, 2018
Q:Does this breaker panel work with GE Q-style thin breakers?
by|Oct 30, 2017
2 Answers
Answer This Question
A: Yes
by|Oct 31, 2018
A: You bet! Note that the standard 1" breakers are THQL, while 1/2" breakers are THQP. It has space for 8 1" breakers or 16 1/2" breakers, according to the catalog at https://www.geindustrial.com/catalog/buylog/01_BuyLog2017_LoadCtrCircBreak.pdf (image attached)
by|Jan 25, 2019
Q:400a service split into 200a main disconnect and this.