#1 Home Improvement Retailer

Questions and Answers for Square D QO 100 Amp 8-Space 16-Circuit Indoor Surface Mount Main Lug Load Center with Cover, Door

Internet #100170999

Model #QO816L100DS

Store SKU #538318

  • QO Interiors and components provide time-tested reliability
  • Compatible with Square D QO standard circuit breakers
  • Includes indoor surface mount cover and aluminum bus bar

Questions & Answers

25Questions
caret
Q:Will this panel take the QO 120 CAFI breakers
by|Dec 6, 2021
1 Answer
Answer This Question

A:  Hello George, Yes, you can use this breaker with a QO load center. Regards, Schneider Electric Customer Care.

by|Dec 8, 2021
    1 found this answer helpful
    caret
    Q:Is this panel the old-style, non-class, CTL QO load centers or the new style that takes the less expensive tandem breakers. Ols style breakers are about 58.00. new style are around 19.00
    by|Dec 15, 2020
    1 Answer
    Answer This Question

    A:  Hello, It will use type QOT tandem breakers. CTL type. Regards, Schneider Electric Customer Care.

    by|Dec 17, 2020
      caret
      Q:Will #6 stranded wire fit into the main lugs of this panel?
      by|Dec 13, 2020
      2 Answers
      Answer This Question

      A:  Yes. The panel is rated for 100 AMPs so 6 guage wire will have no trouble fitting the lugs.

      by|Dec 18, 2020

      A:  Hello, The wire range for the QO816L100DS is #8-#1 for aluminum or copper conductors. Regards, Schneider Electric Customer Care.

      by|Jul 5, 2023
        1 found this answer helpful
        caret
        Q:If I want to use this as a subpanel, do I need to buy zero, one, or two grounding bars? I want to ensure that ground is separated from neutral. Do I need to buy a separate grounding bar for that, or does this box already have that?
        by|Oct 5, 2020
        2 Answers
        Answer This Question

        A:  Hello, If you want to use the QO816L100DS as a subpanel, you need to install a ground bar PK7GTA. Regards, Schneider Electric Customer Care.

        by|Jun 27, 2022
          1 found this answer helpful

          A:  When I bought mine it did not come with a grounding bar and for use as a sub-panel it will need one. The Neutral bar was included.

          by|Mar 29, 2024
          2 found this answer helpful
          caret
          Q:Where can i find just the cover for this. I have an existing one with an open face and would like to buy just the cover. I am unsble to find it
          by|May 3, 2020
          1 Answer
          Answer This Question

          A:  Hello Jason, The cover part number would be 4055345351. Just a heads up though, labeling is not supplied on the replacement cover and the cost of the replacement cover may be close to, or exceed, the cost of a new device. You may want to consider buying a new device and use the new cover on the existing device. Warm regards, Schneider Electric Customer Care

          by|May 7, 2020
            caret
            Q:Can I install this panel upside down?
            by|Aug 25, 2019
            1 Answer
            Answer This Question

            A:  Hello DobermanLA, This load center can be Top Fed, but the load center CANNOT be rotated for bottom feeding. To bottom feed, the incoming wires can enter through the bottom endwall and either go directly into the Main Lugs, depending on the load center interior layout, OR the wires can be fed up past the interior through the gutter area and looped around into the Main Lugs. Regards. Schneider Electric Customer Care.

            by|Aug 26, 2019
              caret
              Q:The installation guide indicates that you can only install tandem qo breakers in spaces that have slots. It does not say that every space has a slot. So, how many tandem qo breakers does this main lug load center hold?
              by|Aug 22, 2019
              1 Answer
              Answer This Question

              A:  Hello, This load center accepts up to 8 tandem breakers.

              by|Aug 26, 2019
                caret
                Q:Can I feed the power to this load center through this breaker: QO 40 Amp 2-Pole Circuit Breaker (Model QO240CP) and if I can, do I remove the main power lugs or just leave them there? Thanks.
                by|May 8, 2019
                2 Answers
                Answer This Question

                A:  Hello, For the QO816L100DS you can use a QO240CP as a branch mounted backfed main. You will also need a PK2MB retaining kit. The main power lugs are not removed. Regards, Customer Care Center

                by|May 17, 2019
                  1 found this answer helpful

                  A:  This should work as long a you do not try to draw more than 40 Amps total from the panel. Otherwise the breaker may trip. Be sure to use wire no smaller than #8.

                  by|May 17, 2019
                    1 found this answer helpful
                    caret
                    Q:IF I HAVE ONE CIRCUIT WITH 2 30 AMP SINGLE-POLE BREAKERS IN IT. WILL IT BE A 60 AMP CIRCUIT.
                    by|Mar 9, 2019
                    3 Answers
                    Answer This Question

                    A:  No, it will be 2 separate 30 amp circuits. The total load will be 60 amps max, but it won't be a single circuit.

                    by|Mar 11, 2019

                      A:  No. If they are on the same circuit with both switches connected/tied together that would make it a double-pole 30 amp 240 volt circuit breaker. A 60 amp breaker is labeled 60 amps.

                      by|Mar 11, 2019

                        A:  Hello John, The tandem QO circuit breakers take one pole space with 2 circuits. It would be (2) 30A circuits. The maximum load would be 60A on the pole space, but would only have (2) 30A circuits. Regards, Customer Care Center

                        by|Mar 11, 2019
                          caret
                          Q:Can this be used as a subpanel in a garage? Or does that require a wet rated panel?
                          by|Nov 27, 2018
                          5 Answers
                          Answer This Question

                          A:  To my knowledge, you do not need a 'wet-rated' panel for your garage since it will not be directly impacted by weather.

                          by|Feb 8, 2019

                            A:  Hello, The QO816L100DS can and has been used as a sub panel. It is a NEMA 1 indoor rated panel. A fully enclosed garage is considered to be NEMA 1 and out of the elements of rain, snow, sleet and ice. Regards, Customer Care Center

                            by|Feb 2, 2021
                              2 found this answer helpful

                              A:  Yes, as long as it's used indoors, it can be used in a garage. A wet rated panel would be used, for example, as a service cutoff for a hot-tub or a breaker panel for a dock.

                              by|Feb 2, 2021
                                1 found this answer helpful

                                A:  I installed this exact panel in my garage as a subpanel. I was able to mount it on the wall behind the main panel on the outside of the garage and run the feed wired straight back through the wall. Be sure to check local electrical codes. I suggest talking with the building inspector who will inspect the installation. I had no trouble at all with this box. I used it to feed a 240 VAC Level 2 charger for my Chevrolet Bolt as also a few utility outlets in the garage.

                                by|Jan 2, 2022
                                  4 found this answer helpful

                                  A:  Yes, this can be used as a sub panel in a garage. I installed this exact one in my home garage. Great product!

                                  by|Dec 14, 2023
                                    1 found this answer helpful

                                    Frequently Bought Together

                                    +
                                    +
                                    Price:
                                    $72.08