Q:Going full 4 wire Marine/RV new install, at 50 amp 120/240, breaking L1/L2/Neutral, No generator in the system (for "only" shore/park power stanchion feeds)... regarding the "pre-packaged with a selection of 4 select circuit breakers" can I choose sizes?
by|May 11, 2024
0 Answer
Answer This Question
Q:DIFFERENCE IN THIS AND THE TM1210CCUBK1 BOX (INTERNALLY)
by|May 11, 2024
0 Answer
Answer This Question
Q:Can I use type QT breakers in this panel?
by|Apr 10, 2024
0 Answer
Answer This Question
Q:Is it possible to purchase just the front cover of the load center?
by|Jan 27, 2024
0 Answer
Answer This Question
Q:is this box 3 phase.?
by|Dec 11, 2023
1 Answer
Answer This Question
A: It is not a 3 phase load center. Try looking for a TL30420C / store sku (1001858481) for a 30 space indoor main lug 3 phase load center.
Thanks for the question.
by|Dec 12, 2023
Q:What's the part number for a second ground bar matching the installed one inside the panel?
by|Dec 6, 2023
0 Answer
Answer This Question
Q:Does this panel come with a 200 amp main breaker
by|Jul 31, 2023
1 Answer
Answer This Question
A: No, this does not include a main breaker. You use this when you have an upstream main breaker, usually outside near the meter socket.
by|Apr 21, 2024
1 found this answer helpful
Q:Hello does this panel lugs are sized that i can use a number 2 wire to feed and make it a.100 amp subpanel
by|Jun 8, 2023
1 Answer
Answer This Question
A: The TLM4020C80GK will accept #1 to 250 kcmil. Thank you for your question.