Q:What would be a recommended grounding wire? #4 Cooper?
by|May 3, 2017
3 Answers
Answer This Question
A: not # 4 but 4/0 (4 ought) there is a difference. That's for your in and out ground. The box it'self doesn't get grounded with a ground wire going to the ground rod.
by|May 4, 2023
A: Hello,
The UHTRS213B will accept (1) #8 - 350kcmil Al/Cu wire for the Main Line, Load and Neutral and (1) #14 - #2 AWG Al/Cu wire for the Ground.
Regards,
Customer Care Center
by|May 4, 2023
A: For a 200 amp service you need a #6 copper, solid or stranded, to at least one ground rod. If the resistance to ground exceeds 25 ohms you must install the second ground rod. You also need a #4 copper or #2 aluminum, solid or stranded, to the metallic water service within 5 feet of where it enters the home. You must jumper around any water meters or pressure reducing valves with the continuous Grounding Electrode Conductor.
by|May 4, 2023
Q:box dimension
by|Jan 8, 2017
1 Answer
Answer This Question
A: UTHRS212B meter socket measures approximately 11'' by 14'' by 4.8''.
Regards, Schneider Electric Customer Care
by|May 4, 2023
1 found this answer helpful
Q:encloseure is it aluminum or steel
by|Aug 16, 2016
4 Answers
Answer This Question
A: High quality steel.
by|May 4, 2023
1 found this answer helpful
A: The enclosure is painted steel.
by|May 4, 2023
A: This is aluminum.
by|Oct 23, 2019
A: Gray-painted steel.
by|May 3, 2023
2 found this answer helpful
Q:what size allen wrench is required to tighten the lugs?
by|Dec 5, 2014
2 Answers
Answer This Question
A: I used an adjustable end wrench. It's Allen on the inside and hex or oct on the outside. You can use an open end wrench.
by|May 4, 2023
A: UHTRS212B lugs utilize both a 1/2'' external Hex nut and a 5/16'' internal allen hex.