Questions and Answers for Square D 80kA Universal Whole Home Surge Protection Device HEPD80

Internet #203540660

Model #HEPD80

Store SKU #1001519416

  • Square D whole home surge protection device rated for 80kA
  • Easy to install - Mounts next to any residential load center
  • 5 Year warranty - $75,000 downstream equipment protection

Questions & Answers

154Questions
caret
Q:Is this type 1 or 2 is is it considered both. I ask because type 2 is required at all panels downstream as well.
by|May 3, 2024
1 Answer
Answer This Question

A:  Hi Aaron, HEPD80 is considered as Type 1 SPD. SPDs investigated for Type 1 applications are automatically suitable for Type 2 applications and may be marked for SPD Type 1 and/or Type 2 applications. "SPD Type 2" are not suitable for Type 1 applications. Warm regards. Schneider Electric Customer Care

by|May 8, 2024
    caret
    Q:My electrical box is outside, can this be mounted externaly?
    by|Apr 21, 2024
    2 Answers
    Answer This Question

    A:  Nathaniel, The HEPD80 carries a NEMA 4X enclosure rating, suitable for both indoor and outdoor installation. Warm regards. Schneider Electric Customer Care

    by|Apr 24, 2024

      A:  Yes, this can be attached to a knock out on the bottom of any brand load center.

      by|Apr 24, 2024
        caret
        Q:I’m mounting the HEPD80 on my siding and need to extend the wire length to reach inside my panel to the breaker. Is it okay to splice all the wires?
        by|Apr 20, 2024
        2 Answers
        Answer This Question

        A:  Homer, In order to help you we need to know more information about your application with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter. Warm regards. Schneider Electric Customer Care

        by|Apr 25, 2024

          A:  Is this an outdoor load center? Why not just attach to the LC via a knock out on the bottom? It's best to have shortest wires possible for best protection.

          by|Apr 24, 2024
            caret
            Q:Will this work for a 200 amp service ?
            by|Apr 17, 2024
            1 Answer
            Answer This Question

            A:  Mack, Yes, it will work. Warm regards. Schneider Electric Customer Care

            by|Apr 19, 2024
              caret
              Q:Can this be installed inside the circuit breaker box?
              by|Apr 2, 2024
              1 Answer
              Answer This Question

              A:  Scott, Yes, below is the instruction bulletin: https://download.schneider-electric.com/files?p_enDocType=Instruction+sheet&p_File_Name=NVE82551_HEPD50-HEPD80_instruction-bulletin_rev05-09-22.pdf&p_Doc_Ref=NVE82551 Warm regards. Schneider Electric Customer Care

              by|Apr 8, 2024
                caret
                Q:What amp breaker should I connect to this
                by|Mar 22, 2024
                1 Answer
                Answer This Question

                A:  Jay, The breakers recommended could be a 2 pole, 15A, 20A or 30A as max, in the closest position to the main breaker. Warm regards. Schneider Electric Customer Care

                by|Mar 25, 2024
                  caret
                  Q:For the 25kva rating which breaker is needed?
                  by|Mar 21, 2024
                  1 Answer
                  Answer This Question

                  A:  Jimmy, Connect the two black wires to a 15A, 20A or 30A 120/240 V twopole circuit breaker, or two adjacent maximum 30 A 120/240 V single-pole circuit breakers within the panel. Warm regards. Schneider Electric Customer Care

                  by|May 6, 2024
                    1 found this answer helpful
                    caret
                    Q:For the 80kA Universal Whole Home Surge Protection Device HEPD80, What Size circuit Breaker in Recommended for a OCPD? The wire size on the SPD is #10.
                    by|Mar 19, 2024
                    1 Answer
                    Answer This Question

                    A:  Craig, Connect the two black wires to a 15A, 20A or 30A 120/240 V twopole circuit breaker, or two adjacent maximum 30 A 120/240 V single-pole circuit breakers within the panel. Warm regards. Schneider Electric Customer Care

                    by|Mar 22, 2024

                      Frequently Bought Together

                      Best Seller
                      +
                      +
                      Price:
                      $125.10

                      Compare Similar Items

                      current item

                      Joules

                      3300

                      2820

                      0

                      3525

                      Maximum Amperage (A)

                      80000

                      0 A

                      140 A

                      100000 A

                      Connection type

                      Panel Mount

                      Panel Mount

                      Panel Mount

                      Panel Mount

                      Electrical Product Type

                      Whole House Surge Protectors

                      Whole House Surge Protectors

                      Whole House Surge Protectors

                      Secondary Surge Protection