Questions and Answers for Eaton CH 60 Amp 120/240 Volts 2-Pole Circuit Breaker

Internet #100208375

Model #CH260

Store SKU #578449

  • Useful in 60 Amp type CH load centers only
  • Robust thermal-magnetic trip curve that avoids nuisance tripping
  • Protects the wiring from overload or short circuit

Questions & Answers

18Questions
caret
Q:Can I use this breaker on a tb panel
by|Jun 5, 2023
1 Answer
Answer This Question

A:  Hello, If you are referring to a Thomas and Betts panels, the CH2100CS would not be UL listed to go into that panel. The CH2100CS is only UL listed to go into Eaton CH panels.

by|Jun 6, 2023
    caret
    Q:Is this actually manufactured by Eaton? I don't see any Eaton/Type CH label.....
    by|May 4, 2023
    1 Answer
    Answer This Question

    A:  Yes Eaton makes the CH breaker. Should have a label on the front of it. 

    by|May 5, 2023
      caret
      Q:Will this work with 6 gage wire
      by|Feb 3, 2023
      1 Answer
      Answer This Question

      A:  Hello, Yes this will work with #6 wire.

      by|Feb 7, 2023
        caret
        Q:I have been looking and waiting for this breaker since Oct.2022 It has not been stocked within 75 miles of my location. Why can't you ship it?
        by|Jan 11, 2023
        0 Answer
        Answer This Question
        caret
        Q:Is the Eaton CH290 2pole breaker in stock anywhere in the USA?
        by|Aug 30, 2022
        1 Answer
        Answer This Question

        A:  Hello, For pricing and availability, you will need to speak with Home Depot customer service. Regards, Eaton

        by|Aug 31, 2022
          caret
          Q:Will a CH breaker work in a Eaton panel that calls for BR breaker
          by|May 24, 2022
          1 Answer
          Answer This Question

          A:  Hello Doug. A CH type breaker will not fit in a load center that calls for BR type breakers. If you need assistance selecting breakers for your specific load center, please contact our Technical Resource Center by phone at 1-877-386-2273 option 2 option 3 option 1 or by email at TRC@Eaton.com. Regards, Eaton.

          by|May 25, 2022
            caret
            Q:Can i use a 2-2-2-4 wire with this breaker to connect it to a sub-panel
            by|Apr 22, 2022
            1 Answer
            Answer This Question

            A:  Hello, This breaker will accept wires sizes #14-#2 for 60 and 75 degrees Celsius Cu/Al wire. You will need to ensure the wire you are using meets these requirements. Feel free to reach out to 877-386-2273 opt 2, 3, 1 if you have anymore questions. Regards, Eaton

            by|Apr 25, 2022
              caret
              Q:What is the range of wire size I can use with this breaker?
              by|Mar 8, 2022
              1 Answer
              Answer This Question

              A:  Hello Nathan. This breaker will accept from a #14 to a #2 copper or aluminum wire. If you have any further questions, please feel free to contact our Technical Resource Center at 1-877-386-2273 option 2 option 2 option 1 or by email at TRC@Eaton.com. Regards, Eaton.

              by|Mar 9, 2022

                Frequently Bought Together

                +
                +
                Price:
                $31.78

                Compare Similar Items

                current item

                Breaker Type

                Double Pole

                Standard

                Double Pole

                Double Pole

                Interruption Type

                Standard Trip

                Standard Trip

                Standard Trip

                Standard Trip

                Mounting Type

                Plug-On

                Plug-On

                Plug-On

                Plug-On

                Series Type

                CH

                Homeline

                CH

                BR

                Connection Type

                Neutral

                Non-Neutral

                Neutral

                Neutral