Q:Is there a comparable product that can support a 125 amp sub panel fully rated?
by|Mar 6, 2023
0 Answer
Answer This Question
Q:Can I plug-in a 125 amp branch circuit breaker in this loadcenter, or is 100 amp the maximum.
by|Feb 17, 2023
1 Answer
Answer This Question
A: Only QPH and HQP breakers installed in the this panel are limited to 100A MAX, when installed on a circuit capable of delivering fault current greater than 10,000A.
Wiring diagram: https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Wiring%20Diagram/SIE_WD_LC_PN4040B-L1200-C.pdf
by|Mar 6, 2023
1 found this answer helpful
Q:Is this panel invertible and fed with the main on the bottom.
by|Dec 23, 2022
3 Answers
Answer This Question
A: The main 200amp On/Off Breaker is located above the 40 slots. My feed wires are coming in from the left side near the top.
by|Sep 9, 2023
A: Yes
by|Jul 3, 2023
A: I can?t figure out any reason that is not allowed to do so, but in most cases, main goes on top.
by|Jul 31, 2023
1 found this answer helpful
Q:What specific branch breaker style types does the siemens model# PN1632B1100C accept?
by|Nov 17, 2022
1 Answer
Answer This Question
A: See the link below for the load center door label for a complete list of approved branch breakers: https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Wiring%20Diagram/SIE_WD_LC_PN1632B1100C.pdf
by|Sep 26, 2023
2 found this answer helpful
Q:Does the Siemens panel model# PN1632B1100C come with a hinged cover door? Does the PN1632B1100C come with a factory installed 100 amp main breaker as well?
by|Nov 17, 2022
1 Answer
Answer This Question
A: The cover/dead front screws mounts to the front of the enclosure and does not hinge on the enclosure. The door to access the breaker when the panel cover is mounted is attached by two plastic hinges. See the link to the cut sheet: https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Specification%20Sheet/SIE_SS_LC_PN1632B1100C-W.pdf?10102022
by|Nov 27, 2022
1 found this answer helpful
Q:Does it come with the 150amp main breaker also or just the panel
by|Nov 2, 2022
1 Answer
Answer This Question
A: Yes this comes with a factory installed 150amp 22AIC main breaker https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Specification%20Sheet/SIE_SS_LC_PN3030B1150C-W.pdf
by|Feb 13, 2023
1 found this answer helpful
Q:Are any Tandem breakers permitted?
by|Oct 31, 2022
1 Answer
Answer This Question
A: This will not accept the Siemens standard type QT tandem breakers. The only tandem breakers this unit will accept are the AFCI tandem breakers type QTA or QTAN. Please see link below to product wiring diagram which lists the acceptable branch breaker types.
https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Wiring%20Diagram/SIE_WD_LC_PN3030B1100C.pdf
by|Feb 13, 2023
Q:Can this 150A MLO plug on neutral be installed in any direction
by|Oct 25, 2022
2 Answers
Answer This Question
A: I don’t see why not. I would say yes.
by|Oct 26, 2022
A: Yes this unit is invertible this allows the you to rotate enclosure so lugs & hubs can accommodate either a top or bottom feed.
https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Specification%20Sheet/SIE_SS_LC_PN3030B1150C-W.pdf
by|Oct 26, 2022
Q:Would this panel be a good replacement for this Seimens Series F in a 200amp manufactured home?
by|Oct 20, 2022
1 Answer
Answer This Question
A: We do not have a record of a F series, but Siemens did make a G series. The G series has been obsolete for a few decades, the PN series and SN series would be the closest current offerings for Siemens Load Centers.
by|Oct 21, 2022
Q:150 amp main breaker pane- is it copper or aluminum buss?