A: It doesnt matter as long as the breaker panel is outdoor rated you and it fits the lugs you have on your panel it is good.
by|Jun 4, 2020
A: Both, you can use it for outside or inside. Its a breaker.
by|Jun 4, 2020
A: Hello Javier,
You can use the QO360 breaker in indoor and outdoor QO load centers.
Regards.
by|Jun 8, 2020
Q:which would be the right box outdoor main lug for two breakers like this
by|Apr 17, 2019
2 Answers
Answer This Question
A: Look up plug in square D out door rated breaker panel and you will find it.
by|Jun 4, 2020
A: Please contact Schneider Electric 888-778-2733 option 2-1-4 to discuss your application.
Regards,
Customer Care
by|Apr 17, 2019
Q:will this work in a cutler-hammer box? thank you
by|Jan 31, 2019
1 Answer
Answer This Question
A: Hello,
The QO breakers have not been tested or approved for use in another manufactures load center. It is not suggested or recommended. It may and can start fires.
Regards,
Customer Care Center
by|Feb 1, 2019
Q:Could this breaker be used to branch off to a sub-panel?
by|Apr 3, 2018
2 Answers
Answer This Question
A: Hello,
The QO3100CP can be used to branch off to a sub panel depending on the load center and application.
Regards,
Customer Care Center
by|May 5, 2023
A: Yes, this breaker can be used to branch off to a sub panel.
by|May 5, 2023
Q:I would like to use this with a pin adapter such as Burndy AYPO 4/0 (has 2/0 pin) adapter. What is the largest solid wire that can be used with this 100 amp breaker?
If the above adapter is too long I will look for angled adapters but I still need to know the max solid (pin) size the breaker will take. Thank you.
by|Jan 7, 2018
1 Answer
Answer This Question
A: Hello,
QO and QOB breakers, 1-, 2- and 3-poles, are UL Listed and rated to accept the following wire sizes, solid or stranded (type B or C). 80 to 125A, 1 wire per lug: (1) #4 AWG - 2/0 kcmil Aluminum or Copper.
Regards,
Customer Care Center
by|May 5, 2023
1 found this answer helpful
Q:What is the maximum size stranded wire that can be used with this circuit breaker? May it be used with aluminum wire?
by|Jan 7, 2018
1 Answer
Answer This Question
A: Hello,
QO and QOB breakers, 1-, 2- and 3-poles, are UL Listed and rated to accept the following wire sizes, solid or stranded (type B or C). 80 to 125A, 1 wire per lug: (1) #4 AWG - 2/0 kcmil Aluminum or Copper.
Regards,
Customer Care Center
by|May 5, 2023
1 found this answer helpful
Q:Can you use this breaker as a back fed main breaker for a main lug type panel
by|Jul 5, 2017
1 Answer
Answer This Question
A: Hello Jim,
Yes, but there are limitations to which load centers they can be installed in.
Regards,
Customer Care Center
by|May 4, 2023
Q:as listed
by|Jun 30, 2017
1 Answer
Answer This Question
A: Hi maximus1,
This item is currently in stock online. The Homedepot.com will allow you to place the order for whatever quantity is available at the time in the online inventory.
Thanks for shopping Home Depot.