Q:Can i puchase a cover with a door for this and not have all the breakers exposed?
by|Nov 22, 2022
3 Answers
Answer This Question

A:  No, per NEC 110, I believe, you are unable to alter original design of "listed" and approved equipment Im not sure if Square D Homeline makes a 100a main lug interior panel with a hinged door. You may have to go with a QO or GE panel for that

by|Jun 28, 2023

    A:  Hi, Yes, for the HOM612L100S, Series 001, Cover- 40558-017-02 (Replacement covers DO NOT have labels, may consider purchasing a new load center). Regards, Schneider Electric Customer Care

    by|Nov 22, 2022

      A:  No can not

      by|Sep 7, 2023
        caret
        Q:I have this panel in a camper that will be fed by power at the campsite. Can I backfeed a two pole 50 amp breaker in this panel to act as a main? Rv cord plugs into a power inlet box (reliance pb50) that is then wired into this panel.
        by|Nov 2, 2022
        1 Answer
        Answer This Question

        A:  Hi, Yes,the 2 pole backfed main breaker must be installed in positions 1 and 2. The maximum backfed branch breaker ampacity that can be used is 100 amperes with catalog number HOM2100. A retaining kit, HOM1RK, must be used to secure the backfed main to the interior. If the load center would be used as service entrance equipment or as the main panel, barrier kit PKSB1HOMBF can also serve the purpose of a retaining kit. Recommended double check with your local authority before the purchase. Regards, Schneider Electric Customer Care

        by|Nov 28, 2022
          1 found this answer helpful
          caret
          Q:Can the HOM2-4l70 be ganged to another HOM2-4l70? My intent is to have one box 110v and the other 240v from separate feeds as a sub panel. Thanks
          by|Nov 1, 2022
          1 Answer
          Answer This Question

          A:  Hi, HOM24L70F/S can be used on 240/120V, and used as service entrace by installing a service disconnect and also be used as as subpanel, but is recommended to check with your local authority the application before installing. Regards, Schneider Electric Customer Care

          by|Nov 28, 2022
            1 found this answer helpful
            caret
            Q:Can I use this as a 40amp service panel? Just need two 20amp breakers for my shed. Will it fit the 40amp breaker as the main?
            by|Oct 28, 2022
            1 Answer
            Answer This Question

            A:  Hi, This device, can be suitable for use as service equipment when service disconnect (main breaker is installed) Note. 70 A maximum branch circuit breaker, 100 A maximum back feed main circuit breaker. Recommended contact your local inspector before the purchase to allow the installation. Regards, Schneider Electric Customer Care

            by|Nov 28, 2022
              1 found this answer helpful
              caret
              Q:this is a three-wire plus ground for a total of 4 wire setup?
              by|Oct 13, 2022
              2 Answers
              Answer This Question

              A:  Hi, Yes, this HOM612L100SCP handles, 2 hots, neutral and the ground bar needs to be purchased separately (PK7GTA). Suitable for use as a service equipment when service disconnect(main breaker) is installed. Regards, Schneider Electric Customer Care

              by|Nov 28, 2022
                1 found this answer helpful

                A:  Yes. 2 - hots, 1 - neutral & 1 - Grd

                by|Jan 27, 2023
                  caret
                  Q:I read where you say not to link the neutral and ground bars. Do I need to drive a seperate ground rod or can I just run 4 conductor cable and ground it to the main panel?
                  by|Sep 6, 2022
                  3 Answers
                  Answer This Question

                  A:  It depends on the code for your area. Mine is the later ,"four conductors grounded to main panel with no connection between neutral" and ground bars in sub panel."

                  by|Sep 10, 2022

                    A:  Robert, The branch neutral conductors should be terminated in the insulated branch neutral assembly terminals. The main neutral should not be bonded to the enclosure in a sub-panel application (i. e. the green neutral bonding screw will NOT be installed). Use a PK__GTA Ground Bar Kit for terminating the equipment ground conductors. Dependent upon the load center in use, the Ground Bar Kit may be factory included, factory installed, or require purchasing separately. NOTE: The Main Neutral Bar in a Square D load center should NEVER be cut or separated for ANY reason. Also, the Branch neutral bars connected to both the left and right side of the Main Neutral bar, should NEVER be disconnected for ANY reason. You need to run separated ground on this subpanel, because on Main Panels the ground and neutral are bonded, contact your local autority before any installation. Regards, Schneider Electric Customer Care

                    by|Apr 15, 2024
                      1 found this answer helpful

                      A:  If this subpanel goes in a separate building you will need a ground rod. If in the same building no additional ground rod is required.

                      by|Sep 9, 2022
                        caret
                        Q:Can a 100 amp main breaker be installed in the 6 space Homeline indoor panel?
                        by|Aug 19, 2022
                        1 Answer
                        Answer This Question

                        A:  Hi, Unfortunately this device is an fixed main lugs, no option to be converted to a main breaker load center. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter. Warm regards. Schneider Electric Customer Care

                        by|Aug 20, 2022
                          caret
                          Q:Can you use 2-pole GFCI breakers (HOM230GFIC and HOM215GFIC) on both these 2-space and 6-space load centers?
                          by|Aug 7, 2022
                          1 Answer
                          Answer This Question

                          A:  Hi, Yes, you can use on the HOM612L100SCP. Regards, Schneider Electric Customer Care

                          by|Jan 26, 2023
                            1 found this answer helpful
                            caret
                            Q:Can you backfeed the 6-space 12-circuit load center?
                            by|Aug 7, 2022
                            1 Answer
                            Answer This Question

                            A:  Hi, The 2 pole backfed main breaker must be installed in positions 1 and 2. The maximum backfed branch breaker ampacity that can be used is 100 amperes with catalog number HOM2100. A retaining kit, HOM1RK, must be used to secure the backfed main to the interior. If the load center would be used as service entrance equipment or as the main panel, barrier kit PKSB1HOMBF can also serve the purpose of a retaining kit. https://www.se.com/us/en/faqs/FA116787/ Regards, Schneider Electric Customer Care

                            by|May 21, 2023
                              caret
                              Q:What size cable do i need to run from my maine panal to this 100amp box to us as a sub panal in my shed
                              by|Jun 27, 2022
                              3 Answers
                              Answer This Question

                              A:  That will depend on the how many amps the breaker is that you are using to run to the subpanel. For instance a 50A breaker would require 8awg wire. 

                              by|Jun 28, 2022

                                A:  When I do the thing I first ask what do you all need to run if it’s just lights a 30amp 4 wire system is enough.   If you want enough for a frig, an air compressor or even a welder once in a while a 60 Amp circuit can be more than prenty. 

                                by|Sep 28, 2022
                                  1 found this answer helpful

                                  A:  Hi, In order to help you we need to know more information about your application with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter. Warm regards. Schneider Electric Customer Care

                                  by|Jul 13, 2022