Q:Not plug on neutral breakers
by|Jan 12, 2022
1 Answer
Answer This Question

A:  Hello Packman, QO612L100SCP accepts only QO Plug-on Circuit Breakers - Not compatible with QO Plug-on Neutral Circuit Breakers. Regards, Schneider Electric Customer Care

by|May 10, 2023
    caret
    Q:It says "single phase"... does that mean for this box you can't have a mix of 120 and 240 breakers using the neutral?
    by|Dec 20, 2021
    7 Answers
    Answer This Question

    A:  This is single phase as opposed to three phase. Yes, you can have a mix a 120 and 240 breakers in this panel

    by|Dec 25, 2021

      A:  Hello SolaProject, In order to help you we need to know more information about it. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter. Warm regards. Schneider Electric Customer Care

      by|Dec 21, 2021

        A:  Single phase is 120/240. Some people think it’s called 2 phase.  You can have 120 or 240 or 12/0/240 circuits in this panel. (If using it as sub panel, you need a separate ground buss bar like the pk7gta. The green screw that comes with the box shouldn’t be used.)

        by|Dec 25, 2021

          A:  You can use both 120 and 240 volt breakers.

          by|Dec 24, 2021

            A:  It can be used for 110 or 220 or both

            by|Dec 25, 2021

              A:  Yes that is how I am using it, for lights and welder.. Don't forget to buy ground bar, it doesn't come with one and for a sub panel the ground and common are separated. Also a ground rod may be necessary.

              by|Dec 22, 2021

              A:  You can mix 120V and 240V circuits in this panel provided that you supply it with 4 wires. 2 hot legs, one neutral and one ground.

              by|Feb 3, 2022
                1 found this answer helpful
                caret
                Q:already have 10-3 under ground and on a 15 amp breaker in the basement
                by|Jun 25, 2021
                2 Answers
                Answer This Question

                A:  Hi Fred, That's exactly what I did. Split my lights and plugs into two circuits, one on each breaker. 15 amp will be fine for the lights and will power small electric hand tools like a drill or hedge trimmer just fine. I have also run a battery charger off that line with no problem.

                by|Jun 25, 2021

                  A:  Hello Fred, Yes, you can use this load center as a subpanel. Regards, Schneider Electric Customer Care.

                  by|Jun 28, 2021
                    caret
                    Q:Do you make some type of door that can be attached to this box so that the breakers are enclosed from the front? If not, is there some other option? Like a plumbers access panel or even something like a silicone iPhone case? Anything that conceals the breakers from view. Thanks!
                    by|Feb 8, 2021
                    2 Answers
                    Answer This Question

                    A:  We offer a similar load center with a door included. Catalog number is QO612L100DS. Regards, Schneider Electric Customer Care.

                    by|Feb 9, 2021

                      A:  The outdoor load center has a cover that flips over it. The part number is QO6-12L100RB. I assume this is for your house. Why not use the Homeline series and save a few bucks. The part numbers are the same, but the pre-fix is changed from QO to HOM. It is important that electrical equipment be installed only by qualified personal.

                      by|Feb 9, 2021
                      caret
                      Q:maybe i overlooked this, but Is there a ground bar included with this sub-panel? I see where Schneider/SqD replied in another question "that a separate ground bar and neutral bar are required in a sub-panel", but no mention whether one is included or not (that I see), OR what the ground bar number(s) is/are for this panel. *From my experience with Square D, the ground bar is not included in main lug panels, but is needed. It makes no sense that I'm having to search for this and wait for an answer...
                      by|Jan 11, 2021
                      1 Answer
                      Answer This Question

                      A:  Hello, Unfortunately, the ground bar is not included in the QO24L70SCP. The catalog number for the ground bar is PK4GTA or PK4GTACP. Regards, Schneider Electric Customer Care.

                      by|Dec 18, 2021
                        1 found this answer helpful
                        caret
                        Q:WANT TO USE 120 VOLT SERVICE
                        by|Nov 7, 2020
                        5 Answers
                        Answer This Question

                        A:  Single pole breakers up to 2 of them

                        by|Dec 18, 2021
                        1 found this answer helpful

                        A:  I've used a 25 and 20 amp breakers, single pole. Total of 2. Used this box 3 different times.

                        by|Mar 26, 2024
                        1 found this answer helpful

                        A:  What are you suppling current to with this load center? 30 amps means largest conductor (wire) size is #10. Generally, you could use 2 30amp breakers (bridged) or 2 separate 15amp breakers.30amps/240 volts is common for electric water heaters.

                        by|Dec 18, 2021
                        2 found this answer helpful

                        A:  Hello Harry, A QO single pole breaker is ok for 120 VAC. You can use two of them maximum in this load center. This is a 2 space/2 circuit panel, accepting full size QO branch circuit breakers only. The 30 ampere panel rating should not be exceeded, or 25 ampere when aluminum feeder wire is used. Warm regards, Schneider Electric Customer Care

                        by|Dec 18, 2021
                          1 found this answer helpful

                          A:  It will not accept type QO-EPD, QO-GFI, QO-AFI, QOB, QOT tandem or QO tandem circuit breakers.

                          by|Aug 22, 2022
                            1 found this answer helpful
                            caret
                            Q:How can I feed a 30A wire to two 15A breakers with this load center? It look like the two hot input terminals of this load center are not connected. Using a jumper wire doesn't feel right to me.
                            by|Sep 25, 2020
                            2 Answers
                            Answer This Question

                            A:  The black wire to one breaker and the white wire to the other to have to hot 15 amps.

                            by|Oct 12, 2022

                              A:  Hello, For wiring and installation of breakers, you can contact a local inspector or electrician and follow your local NEC code requirements. Regards, Schneider Electric Customer Care.

                              by|Sep 25, 2020
                                caret
                                Q:Square d qo with 6 30 amp breakers
                                by|May 30, 2020
                                2 Answers
                                Answer This Question

                                A:  Super value!

                                by|Oct 17, 2021

                                  A:  Hello Rickey, The wire range for the QO612L100SCP is #8-#1. You can use aluminium or copper wire. For the breakers, you have to plug them into the busbar. In case you require a ground bar, you can use the PK7GTA. Regards.

                                  by|Jun 1, 2020
                                    caret
                                    Q:What size clamp connector should I use? Thanks
                                    by|Apr 27, 2020
                                    2 Answers
                                    Answer This Question

                                    A:  Hello Jess, the QO2L30S has 0.50", 0.75", 1.00" concentric knockouts Regards, Schneider Electric Customer Care.

                                    by|May 1, 2020

                                      A:  You will probably feed the box with 10/3 w/g and that usually calls for a 1" clamp. If the wire leaving the box is also 10/3 w/g, again you'll use a 1" clamp. If the circuit breaker is 15 or 20 amp and the wire leaving the box is #12 or #14, you can use a ½" clamp.

                                      by|Apr 30, 2020
                                      1 found this answer helpful
                                      caret
                                      Q:Per the rating of this indoor main lug load center, what is the required feeder wire thart will feed this load center of of our houses main sertvice panel. Is 10/3 with ground, 10/2 with ground,I have some 6/2 with ground could that be utilized , no biggie just asking,. Thank You for your answers!
                                      by|Apr 11, 2020
                                      3 Answers
                                      Answer This Question

                                      A:  Hi Hempifier: It depends on whether the breaker(s) you put into the box are single-pole or double-pole, and whether the device(s) it serves require a neutral wire. If you use a 30-amp double-pole breaker to supply a dryer with a 3-wire plug, then 10/2 with ground is OK. It is also OK to use a larger wire like 6/2 with ground. If your breakers are single-pole, or if you use a double-pole breaker to supply a device that requires a neutral wire (like a hot tub heater) then you'll need to feed the box with separate neutral and ground wires to stay within the code. Make sense? Maineiac

                                      by|Apr 11, 2020

                                        A:  Nothing smaller than 10 gauge wire should be use! 30 amp breaker’s are rated at least 10g! However, anything greater is just overkill for this box!

                                        by|Jan 8, 2024

                                          A:  Hello Hempfier, The wire range for the QO2L30SCP is #12-#10 if you use aluminium wire or #14-#10 if you use copper wire. If you need a ground bar for the load center, you can use the PK3GTA1. Regards.

                                          by|Apr 15, 2020