#1 Home Improvement Retailer

Questions and Answers for Square D Homeline 20 Amp Single-Pole Combination Arc Fault Circuit Breaker (12-Pack)

Internet #313219936

Model #HOM120CAFIC12

Store SKU #1005370697

  • The CAFCI design protects against parallel and series arcs
  • Built in Time Saver Diagnostics allows easier troubleshooting
  • Compatible with Square D Homeline electrical panel and CSEDs

Questions & Answers

170Questions
caret
Q:Will 8 gauge stranded wire fit in this breaker terminal ?
by|Sep 23, 2023
1 Answer
Answer This Question

A:  Hi, The wire range is: Al - 14–8 AWG CU - 14–8 AWG or (2) 14–10 AWG Warm regards. Schneider Electric Customer Care

by|Dec 2, 2023
    caret
    Q:Will this grd fault breaker work in a ITI panel?
    by|Sep 12, 2023
    1 Answer
    Answer This Question

    A:  Hi, Unfortunately No. Each manufacturer has it's own UL listings for their specific products based on their specific product line and their specific combination of products. Warm regards. Schneider Electric Customer Care

    by|Oct 14, 2023
      caret
      Q:My house was built in 1945. I have numerous two wire outlets that do not have grounds Can i use a GFCI on those circuits and then just install a normal 3 wire outlet?
      by|Aug 29, 2023
      1 Answer
      Answer This Question

      A:  Hi, In order to help you we need to know more information about your application with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter. Warm regards. Schneider Electric Customer Care

      by|Aug 31, 2023
        caret
        Q:Do I need to have a GFCI receptacle for my washing machine if I am using a Homeline combination AFCI breaker?
        by|Jul 24, 2023
        2 Answers
        Answer This Question

        A:  Yes the washer has to be gfci protected. You can use a dual function AFCI/GFCI breaker or if you already have a combination AFCI breaker installed you will need a GFCI receptacle. The receptacle has to be readily accessible and not down behind the washer.

        by|Jul 25, 2023

          A:  Hi, CAFI breakers include the combination of both parallel and series arc fault protection, which helps to protect against fire hazards caused by arcing in damaged electrical wiring (UL1699 Combination AFCI). They have a white test button, so, if the washing machine needs to be gfi protection, yes you can include the GFI receptacle or Dual Function Breaker. GFI breakers include 5 mA ground fault protection, which helps to protect people from being seriously injured if electricity should flow through their body to ground (UL943 Class A GFCI). They have a yellow test button. DF breakers include the dual protection of both of the above, GFI and CAFI, in one device. They have a purple test button. Regards, Schneider Electric Customer Care

          by|Dec 25, 2023
            1 found this answer helpful
            caret
            Q:does a square d breaker fit a e t n breaker box
            by|Jul 21, 2023
            1 Answer
            Answer This Question

            A:  Hi, Unfortunately No. Each manufacturer has it's own UL listings for their specific products based on their specific product line and their specific combination of products. Regards, Schneider Electric Customer Care

            by|Jul 26, 2023
              caret
              Q:What type of Homeline circuit breakers do I need to properly fit the new HOM816M200PFTRB 200a feed through panel I just bought from Home Depot. There were 3 types of homeline breakers in the store and none of them seem to fit this panel.
              by|Jul 5, 2023
              1 Answer
              Answer This Question

              A:  Vince, HOM816M200PFTRB accepts the next breakers: Homeline Standard Plug-On Circuit Breakers - Table 1.40: Standard HOM Plug-on Circuit Breakers Homeline Ground-Fault Circuit Breaker (HOM-GFI) - Table 1.42: HOM-GFI Circuit Breakers Homeline Combination Arc Fault Circuit Interrupters (HOM-CAFI) - Table 1.43: HOM-CAFI Circuit Breakers Homeline Dual Function Circuit Breaker (HOM-DF) - Table 1.44: HOM-DF Circuit Breakers Homeline Tandem and Quad Tandem Circuit Breakers (HOMT) - Table 1.46: HOMT Tandem Circuit Breakers Link below: https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=0100CT1901_SEC-01.pdf&p_Doc_Ref=0100CT1901_SEC-01&_ga=2.105099843.1371177036.1673289917-2095425866.1667836878 Regards, Schneider Electric Customer Care

              by|Jul 5, 2023
                caret
                Q:what homeline 20 amp CB do I need for Square D Panel QOC 20MW
                by|Jun 4, 2023
                4 Answers
                Answer This Question

                A:  You need the QO type breaker.  Not the Homeline type.  Both are made by Square D, but mount on different types of bus bars in the panels.  

                by|Oct 9, 2023
                  1 found this answer helpful

                  A:  Hi, QOC is the cover for a QO Load Center, and only accepts OQ breakers like the QO120 - single pole or QO220 - double pole. Regards, Schneider Electric Customer Care

                  by|Jun 5, 2023

                    A:  If I understand correctly, you have a QO panel? If so, Homeline breakers don't fit in a QO panel, you need a QO breaker.

                    by|Jun 24, 2023

                      A:  You cannot use a homeline breaker in this panel, You will need a QO120

                      by|Jun 8, 2023
                        caret
                        Q:What Homeline 15 amp ground fault circuit breaker do I need for a Square D Panel QOC30MG225.
                        by|May 30, 2023
                        1 Answer
                        Answer This Question

                        A:  Hi, QOC30MG225 is just for the door, the interior catalog number will be needed to double check, below an FAQ to how locate this info: https://www.se.com/us/en/faqs/FA274608/ You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter. Warm regards. Schneider Electric Customer Care

                        by|Jun 3, 2023
                          1 found this answer helpful
                          caret
                          Q:What does the "CP" at the end of mean? I need a 40 amp breaker but on SE website it has two models HOM140 and HOM140CP. Are they interchangeable?
                          by|May 28, 2023
                          1 Answer
                          Answer This Question

                          A:  Hello JoeyTrucker, The CP stands for commercial packaging. The breaker itself is no different. Regards, Schneider Electric Customer Care

                          by|May 31, 2023
                            1 found this answer helpful
                            caret
                            Q:Is home line compatible with Cutler Hammer?
                            by|May 18, 2023
                            1 Answer
                            Answer This Question

                            A:  Hi, Unfortunately no, each manufacturer has it's own UL listings for their specific products based on their specific product line and their specific combination of products. Regards, Schneider Electric Customer Care

                            by|May 18, 2023

                              Frequently Bought Together

                              Top Rated
                              +
                              +
                              Price:
                              $636.55

                              Compare Similar Items

                              current item

                              Breaker Type

                              Standard

                              Standard

                              Standard

                              Standard

                              Interruption Type

                              AFCI

                              AFCI

                              AFCI

                              AFCI

                              Mounting Type

                              Plug-On

                              Plug-On

                              Plug-On

                              Plug-On

                              Series Type

                              Homeline

                              Homeline

                              QO

                              QO

                              Connection Type

                              Non-Neutral

                              Non-Neutral

                              Pigtail

                              Non-Neutral