Q:Is it the same as an Eaton CHN220GF? Installed in a Cutler Hammer CH12BBR TYPE 3 R Enclosure panel
by|Aug 3, 2024
2 Answers
Answer This Question
A: No, This is a Square D product. Not compatible with Eaton.
by|Aug 5, 2024
A: Hi Kent,
It is the same electrically on the CHN220GF however, you can't mount our breakers to Eaton panel/enclosure. Reason being is that every product has it's own UL testing and listing and our products have not been tested with Eaton products.
Warm Regards,
Schneider Electric Customer Care
by|Aug 5, 2024
Q:Will this replace a type d dw 8586 breaker?
by|Aug 3, 2024
1 Answer
Answer This Question
A: Hi Matt,
Type DW-8586 is an issue number it varies depending on the batch of production and has nothing to do with the breaker dimension and installation. If you are needing 2 pole 40A breaker for HOMELINE then this is the correct breaker. The CP suffix is only for Commercial Packaging which is the type of packing seen in retail stores it is no different on a HOM240 breaker.
Warm Regards,
Schneider Electric Customer Care
by|Aug 5, 2024
Q:Can I put this in the square D A/C disconnect box non-fusable?
by|Jul 28, 2024
1 Answer
Answer This Question
A: Hi Dglivin,
In order to help you we need to know more information about your application with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter.
Warm regards. Schneider Electric Customer Care
by|Jul 31, 2024
Q:I have a square d load center, bought and INSTALLED, and these are not available in store OR ONLINE?! the box you sold will ONLY accept these! This is unacceptable
by|Jul 23, 2024
1 Answer
Answer This Question
A: Hello BMSMF,
We are sorry for the inconvenience this has caused you. In case you are having an issue looking for HOM230CP, you may try HOM230 instead. The CP suffix stands for commercial packaging. The breaker itself is no different.
Warm regards. Schneider Electric Customer Care
by|Jul 23, 2024
Q:Old (70s) SqD fused 30A plug switch (not sure rating) feeding a mini panel currently 2x15A 110v sp breakers. Like to connect 40A 240V point-of-use tankless, and keep 1+ 115V 15A for lighting. Any possible way?
by|Jul 17, 2024
1 Answer
Answer This Question
A: Hi BobMac,
If you have a 30A plug switch and the loads you are intending to use is (1) 40A and (1) 15A the plug switch will overload. It may be best to replace the plug switch first with a higher rated one before doing the application you want.
Warm regards. Schneider Electric Customer Care
by|Jul 18, 2024
Q:Will this work as a breaker in my combo meter/service entrance model RC81F200CA200. It would me in the service panel to supply power to the shed. (not as the main 200 amp breaker but the feed breaker under the main 200amp breaker)
by|Jul 8, 2024
1 Answer
Answer This Question
A: Hi John,
If you have an RC81F200CA200 then most probably that has a HOMELINE type interior so that particular breakers linked will work. However, it may still be best to take a photo of the wiring diagram on the back of the cover and reach us out with our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter.
Warm regards. Schneider Electric Customer Care
by|Jul 12, 2024
Q:What number of wire should I use for this tank
by|Jun 12, 2024
1 Answer
Answer This Question
A: Hello Andres,
The HOM240CP has a wire range of 1 wire per lug: (1) #8 - #2 AWG Aluminum or Copper. Typical water tank usually requires 30A 2 pole breaker and 2 #10 wires. In order to verify this to you, we need to know more information about your application. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter.
Warm regards. Schneider Electric Customer Care
by|Jun 12, 2024
Q:Can I use 12/2 romex to wire this breaker for a 18,000 btu Mr cool mini split?
by|Jun 11, 2024
2 Answers
Answer This Question
A: Yes you can use 12/ 2 with ground. A 20 amp 2 pole breaker. A mrcool mini uses under 20 amps
by|Jul 16, 2024
A: Hello Becca,
This breaker has the following wire range:
1 wire per lug: (1) #14 - #8 AWG Aluminum or Copper
2 wires per lug: (2) #14 - #10 AWG Copper
So you can have a 12/2 Romex in the HOM230CP.
Warm regards, Schneider Electric Customer Care
by|Jun 11, 2024
Q:Is this breaker compatible with an Eaton type BR 2 pole GFCI breaker # GFTCB250?
by|May 21, 2024
1 Answer
Answer This Question
A: Hello Scott,
We both have a 50A GFCI breaker for the Homeline and QO load center. HOM250GFI and QO250GFI. Please take note that you cannot use a third-party breaker for Square D Panels. This will be a violation of the UL listing and the warranty of the product.
Warm regards. Schneider Electric Customer Care
by|May 21, 2024
Q:Are homeline breakers rated 90 degrees C?
by|May 9, 2024
1 Answer
Answer This Question
A: Hi Dwayne,
The 40 - 125 A Homeline breaker lugs are all rated at 75 degrees C. 90°C conductors may be used if installed in accordance with the 75-degree C wire tables of the current NEC (National Electrical Code).
The 15 - 35 A Homeline breaker lugs are dual-rated 60/75 degrees C.
Regards,
Schneider Electric Customer Care