Questions and Answers for ABB 60 Amp 8-Space 4 Circuit Spa Panel Main Lug Load Center (TL412R260GF)

  • GE residential electrical products is switching to ABB
  • 60A 2-pole 240V GFCI Breaker included
  • Unit has 2-additional 1in. spaces for extra circuits

Questions & Answers

IS THERE A COMPATIBLE SEIMENS CIRCUIT BREAKER THAT WILL FIT IN THIS PANEL
ByApr 23, 2020
3 Answers | 
Answer This Question

You may be able to fit a seimens breaker in this panel but it is a code violation because it is not listed for a seimens breaker.

By|Feb 2, 2021

Yes, there are several breakers that will fit in this panel.

By|Aug 18, 2020

    No, Midwest Electric Products is a GE company and only UL Listed for use with GE circuit breakers. To use a Siemens breaker in this disconnect would be a code violation.

    By|Aug 12, 2025

    (6)

    Can this panel be fed from the top?
    ByMar 13, 2020
    5 Answers | 
    Answer This Question

    Thank you for your question. Yes, the UG412RMW260P can be fed from the top. Top feed would require a rain tight hub. Part numbers 1” TC100P, 1 1/4” TC125P, 1 1/2” TC150P, 2” TC200P.

    By|Jul 17, 2020

      (3)

      yes there is an access panel on the top

      By|Jun 27, 2021

        This panel can be fed from the top. Whenever feeding from the top in a NEMA 3 enclosure it is important to use a hub. Purchased separately. This will insure a water tight fit and maintain the UL listing.

        By|Feb 2, 2021

        It IS possible, but it would not be waterproof if you do, and you would have to drill a hole since there is none that exists.

        By|Aug 18, 2020

          Yes, this NEMA 3R panel can be fed from the top when using a GE hub.

          By|Aug 18, 2020

          (4)

          what are the size and quantity of cutouts on the Bottom of this unit
          ByOct 31, 2019
          2 Answers | 
          Answer This Question

          The sizes are 1/2", 3/4" and 1". To see the number of knockouts I'd recommend you visit your local HD store and ask the electrical dept manager to show you.

          By|Aug 18, 2020

          (5)

          There are 3 -1/2”, 2 - 3/4 “, 3-1”, 1-1-1/4”, 1-1/2” and 2” . This is all available knockouts however 3 of the 4 knock outs are concentric meaning they are combination. 2 go from 1/2” through 1”. 1 goes from 1” through 2”. The 4th is only 1/2”. Hope this helps.

          By|Aug 18, 2020


            60 amp gfci breaker keep tripping any one have pictures for right connection
            BySep 6, 2019
            2 Answers | 
            Answer This Question

            No pictures, but correct connections are not rocket science. You never mentioned if the breaker ever worked properly so I am assuming you just connected it incorrectly. First of all, the disconnect should be fed with 4-wires, 2 hots, 1 neutral and 1 ground to the ground bar, the same as any 120/240 volt subpanel. The white pigtail from the breaker should terminate on the neutral bus. The 2 hot circuit conductors and the neutral circuit conductor (if there is one) are the load conductors and all 3 terminate at the appropriate terminal on the GFCI breaker. There should be instructions detailing this. The circuit grounding conductor terminates on the ground bar. If the breaker continues to trip, remove all load conductors from the breaker and try resetting again. If the GFCI breaker trips with no load conductors connected it is faulty and should be replaced.

            By|Aug 18, 2020

            (5)

            On the load side wiring the red and black wire go to the right and left breaker screws. The load neutral, (white) goes to the center breaker screw. The most common mistake is terminating the load neutral to the neutral bar vs the breaker. This will cause it to trip.

            By|Feb 2, 2021


            If I my a lower amperage breaker in addition, does that breaker also have to be gfi or will the main breaker handle the gfi for all additional breakers? Thanks
            ByMay 16, 2019
            6 Answers | 
            Answer This Question

            This spa panel is a 125 amp rated main lug only panel, the 60 amp GFCI breaker is a branch breaker and not a main breaker so no, the GFCI breaker does not protect other circuits in the panel. You can add an additional GFCI breaker or if in the case of a receptacle circuit, you can add a regular GE THQL breaker and use a GFCI receptacle to provide the required GFCI protection.

            By|Apr 17, 2021

            (7)

            Thank you for your question. The GFCI is dedicated to the 60a 240v SPA. It’s not a main. There are two additional spaces for other breakers that can be installed. You can add an additional GFCI breaker for another circuit. THQL1120GFTP or THQL1115GFTP for 120v circuits.

            By|Apr 17, 2021

              (4)

              I understand your question ,,,referring to the 60amp breaker as the main breaker and any other breakers added in the box for what ever use--"WOULD THE 60 amp PROTECT ANY ADDED BREAKERS ?" , ,, my turn now, - The item needing the 60amp GFI breaker will actually be connected to it by the neutral wire from the item needing the breaker-- just under the 2 connectors (red,black) or the 2 legs of 120v) on the breaker , ,, the white pig tail coming from the breaker will connect to the neutral bus bar, as will the neutral from the power source, The power source will connect to the separate large connectors mounted in the box for each one of them. for each one of the 120v wires (red) (black) (each leg of the 220)). This should describe that the neutral wire going to the item needing the 60am GFI is dedicated ONLY between that breaker and item needing the breaker. All additional breaker slots or spots etc. in this box may be non gfi,, DEPENDING WHAT THEY ARE NEEDED FOR.

              By|Apr 17, 2021

                No, this 60 Amp, GFIC breaker is dedicated to the spa because it is 2-pole 240 Volt. There are no spaces for additional breakers in this panel.

                By|Apr 17, 2021

                  The included breaker will only protect the circuit that is connected to it. It WILL NOT protect any other circuits installed in the panel. You will need a separate GFCI breaker or feed into a GFCI receptacle and use the feed through wiring of the receptacle to protect that circuit.

                  By|Apr 17, 2021

                  (1)

                  Any breaker installed after the GFCI Disconnect should be covered by GFCI Breaker

                  By|Apr 17, 2021


                    I am putting in a pottery kiln for my wife in her she shed. The kiln draws 47 amps x125% which equals 58.75 amps. Will this panel satisfy the GFCI requirements here for a GFCI if outdoors? I will be wiring it directly from the c/b panel 60 amp breaker.
                    ByDec 21, 2018
                    5 Answers | 
                    Answer This Question

                    Looks like it should. One more thing, if the kiln controller is relay based, you should probably avoid arc fault breakers in this circuit, because the relays arc a bit when they open and close and could trip an arc fault breaker (AFCI). Newer style controllers are electronic, and shouldn't have this problem.

                    By|Aug 18, 2020

                    (2)

                    There is no GFCI requirement for a kiln. Keep in mind that you are only allowed one power feed to a detached building so if you would like some lights and perhaps a few 120 volt receptacles you will need a larger circuit to the shed. I would recommend you install a 100 amp main breaker panel with an added ground bar kit and feed it with 3 - #4 THWN and 1 - #8 Grn THWN (ground) from an 80 amp breaker in the main house panel. You'll also need to install at least one ground rod and connect it to the panel ground bar with #6 copper ground wire. The 100 amp main breaker becomes a disconnect and protection is at the 80 amp breaker in the house. You can now install a 60 amp breaker to feed the kiln. If the shed has a bare concrete floor the receptacles will need to be GFCI protected.

                    By|Aug 18, 2020

                    (7)

                    Jared.....in view of the latest information you posted, the kiln still should not need GFCI protection, but the receptacles might since the floor doesn't seem to me to be finished. It's really a judgement call on the part of the inspector. I think I would go ahead and GFCI protect the receptacles using a GFCI receptacle. Even if the inspector requires you to GFCI protect the kiln circuit, you do not need this separate panel, just install the GFCI breaker in the GE main service panel. That being said, the least expensive way to buy a GE 60A GFCI breaker is to buy either a GE or Midwest spa panel w/GFCI breaker, remove the breaker and throw the enclosure away. A breaker alone will cost more than either of the spa panels that come with the GFCI breaker. This all depends on the version of the NEC your town has adopted and the inspector makes the final call.

                    By|Aug 18, 2020

                    (6)

                    Yes it will satisfy the National Electrcal Code and most local codes for breaker sizes and GFIC. Also, the enclosure is NEMA 3R for outdoor use.

                    By|Aug 18, 2020

                      (2)

                      TomB2......Thanks for your response. I have a new 200amp feed coming directly to the shed, separate from the house, with its own meter. The kilnwill be on a wood floor protected with cement board. Will that require a GFCI? Merry Christmas Tom!

                      By|Aug 18, 2020

                        (2)

                        Is this panel CSA certified as well
                        ByOct 16, 2018
                        2 Answers | 
                        Answer This Question

                        No, this spa panels is UL Listed, but not CSA listed. For a CSA Listed spa panel I suggest you visit the Home Depot Canada website here: https://www.homedepot.ca/en/home/p.spa-panel-with-factory-installed-2p-60a-ground-fault-ci.1000170982.html

                        By|Aug 18, 2020

                        (5)

                        My panel, made by Midwest, is not CSA certified.

                        By|Jul 17, 2020

                          (4)

                          What type of breaker does this panel take?
                          ByJun 19, 2018
                          2 Answers | 
                          Answer This Question

                          This panel takes GE Type THQL or Type THQP breakers

                          By|Aug 18, 2020

                          (5)

                          60 amp

                          By|Aug 18, 2020


                            Compare Key Features

                            current item

                            Product Snapshot

                            Ideal for outdoor spa setups, this 60 Amp GFCI spa panel ensures safe and compliant installations.
                            Ideal for outdoor spa setups, this spa panel offers 60A GFCI protection and NEMA 3R weather resistance.
                            Ideal for outdoor spa/hot tub use, ensuring safety and weather resistance.
                            Ideal for evaporative cooler applications, this disconnect offers fused protection and a weatherproof NEMA 3R enclosure.

                            Voltage Rating

                            240 V
                            120/240 V
                            120/240 V
                            240 V

                            Amperage Rating

                            60 Amp
                            60 A
                            50 A
                            40 A

                            Fuse Protection

                            Weather Resistance

                            UL Certification