Does the gfi breaker have a lug on it for a neutral wire to run to the spa
ByAug 8, 2016
4 Answers | 
Answer This Question

The panel has the the spot for the neutral. As well as the ground. The breaker just handles the hot feed. In this case the red and the black.

By|Oct 16, 2020

    TomB2's answer is correct. The breaker will not operate if wired incorrectly.

    By|Jul 17, 2020

      (5)

      Yes. It is important to make the load neutral connection to the breaker and not the neutral bus or it will trip.

      By|Feb 2, 2021

      Yes, the GFCI breaker has 3 lugs to terminate the 2 hot wires and the neutral wire.

      By|Aug 18, 2020

      (5)

      My panel has a bonding strap screwed to thw middle of the box, what do I do with it?
      ByJun 15, 2016
      2 Answers | 
      Answer This Question

      Nothing , if it is a sub panel. The neutral and ground are not tied togther after they leave the main disconnect panel.

      By|Jul 17, 2020

        (3)

        Remove it and throw it away. A bonding strap is only used when the equipment is used as a service entrance panel.

        By|Aug 18, 2020

        (6)

        What is the purpose and use of the ground rod mounted to the back of the panel?
        ByJun 15, 2016
        2 Answers | 
        Answer This Question

        To attach to an earth ground rod.

        By|Aug 18, 2020

          There is no ground rod with this panel. A ground rod is a minimum of 8 feet long. Please reword your question and resubmit.

          By|Aug 18, 2020

          (5)

          I am no longer using this panel for a hot tub. I am interested in adding 2 single pole 20 amp breakers to this box to now feed an above ground pool and add the other 20 amp for plugs around the deck-is this doable by just adding the 2 20 amp breakers to existing box and running the wires?
          ByJun 8, 2016
          3 Answers | 
          Answer This Question

          Yes, no problem. You will need to make sure those circuits are GFCI protected. This is critical. Either install 1 pole 20 amp GFCI breakers or feed a normal breaker into a GFCI receptacle and wire off the load side of the receptacle to protect the circuit.

          By|Feb 2, 2021

          Assuming you are removing the 60 amp breaker, and adding 20 amp gfci breakers, and properly encasing or burying the correct size wires, this will do what you want. You have space to add 4 single pole breakers so you can run 4 circuits.

          By|Jul 17, 2020

            (4)

            In short, it depends. If you do run the proper wires within a reasonable distance (less than 70 feet from the breaker panel) and the correct breakers, then you can. However, it's always best to go by any other factors with a local electrician in your area. Even if won't go under an inspection, it can and will eventually, so safety and code compliance is key. Joseph

            By|Aug 18, 2020


            Does the 60 amp gfi breaker have a neutral load attachement screw?
            ByMay 18, 2016
            2 Answers | 
            Answer This Question

            Yes, there is a terminal for the "Load" neutral on the GFCI breaker.

            By|Aug 18, 2020

            (5)

            The breaker only handles the hot load. The panel takes care of the neutral and ground.

            By|Aug 18, 2020


              my hot tub will require 4 wires 2 hot a neutral and a ground, most spa disconnects I have seen have a neutral on the breaker but this one does not, is this the right panel or do I need to get another one?
              ByApr 11, 2015
              2 Answers | 
              Answer This Question

              The spa needs ground fault circuit interrupter (GFCI), and overload protection. These can be combined in one breaker or two, one for the overload protection and one for the GFCI protection.

              By|Jul 17, 2020

              (1)

              I found it, the neutral was on the back side of the breaker odd place for it but it is there

              By|Jul 17, 2020

                (5)

                Can I get an on-line wiring diagram for Model # UG412RMW260P?
                ByJun 30, 2014
                2 Answers | 
                Answer This Question

                There should be a complete wiring diagram in the installation instructions for your spa.

                By|Aug 18, 2020

                (5)

                Dear Valued Home Depot Customer, We reached out to the MFG for more information and find the wiring diagram attached.

                By|Aug 18, 2020
                0/0


                specification indicates life time waranty is this also aplicable to the 60 amp gfi?
                ByFeb 26, 2014
                2 Answers | 
                Answer This Question

                Yes

                By|Aug 18, 2020

                (5)

                Thank you for your recent inquiry with The Home Depot. Yes, this item is covered by a Lifetime Manufacturer's Warranty. For any other questions, please call us at HomeDepot.com Customer Service 800-430-3376.

                By|Aug 18, 2020

                (6)

                Compare Key Features

                current item

                Product Snapshot

                Ideal for outdoor spa setups, this 60 Amp GFCI spa panel ensures safe and compliant installations.
                Ideal for outdoor spa setups, this spa panel offers 60A GFCI protection and NEMA 3R weather resistance.
                Ideal for outdoor spa/hot tub use, ensuring safety and weather resistance.
                Ideal for evaporative cooler applications, this disconnect offers fused protection and a weatherproof NEMA 3R enclosure.

                Voltage Rating

                240 V
                120/240 V
                120/240 V
                240 V

                Amperage Rating

                60 Amp
                60 A
                50 A
                40 A

                Fuse Protection

                Weather Resistance

                UL Certification