Q:What are the requirements for the inside wall unit size & space wise. That is how much headroom is needed above the unit or below and on each side to enable proper install and adequate AC coverage? Thanks.
by|Jan 19, 2019
2 Answers
Answer This Question

A:  Thanks, great question, you need to leave about 2 to 3 inches on the top side of the unit being that is where the unit is drawing in the air. The sides are not as critical as the top, and the bottom should be free of obstructions by approximately 12 inches due to the air coming out of the bottom front portion. We highly recommend having the unit mounted minimal 6 feet up the wall due to the air flow coming from the bottom front of the unit for maximum airflow. Also keep in mind these units are sized by sqft, and the 24,000 Btu is good for up to 1200 sqft.

by|Jan 21, 2019

    A:  Based on the way my unit is installed, I would suggest a space of 3 feet from the ceiling and have ample room on the sides. I hope this helps.

    by|Jan 21, 2019
      caret
      Q:What is the amperage for this unit?
      by|Jul 20, 2018
      2 Answers
      Answer This Question

      A:  The unit uses 7.4 amps to cool and 9 amps to heat.

      by|May 5, 2023

        A:  As indicated under Specifications > Details on the product's page before the BTU Cooling/Heating Ratings, the average current (amperage) for this unit is 11 amps.

        by|Oct 27, 2023
          caret
          Q:What size circuit breaker is required?
          by|Jul 14, 2018
          2 Answers
          Answer This Question

          A:  A 20amp breaker is recommended.

          by|Nov 4, 2022

            A:  This product requires a minimum of a 30 amp circuit breaker.

            by|May 25, 2023
              2 found this answer helpful
              caret
              Q:i only have available 208 volts, will this system run off that?
              by|Jun 25, 2018
              2 Answers
              Answer This Question

              A:  Yes

              by|May 5, 2023

                A:  Yes, you can run off of 208v. You just loose a little bit of the efficiency.

                by|May 5, 2023
                  caret
                  Q:can you run the freon lines up to 45 feet for this unit
                  by|Jun 25, 2018
                  1 Answer
                  Answer This Question

                  A:  Yes, you can. You would just need to add some refrigerant to accommodate the extra line. There is a chart is the owners manuals on how much to add.

                  by|May 5, 2023
                    caret
                    Q:can this be installed by home depot workers?
                    by|Jun 21, 2018
                    2 Answers
                    Answer This Question

                    A:  My grandson and I installed this in about 6 hours. He is licensed to install A/C units, but this was the first of this kind for him to install. We covered the outside hoses with sheet metal matching the existing house and everything looks "first class" outside and inside. We installed it in the Spring so we have used both heat and air and are very happy with the unit. It does require some work and figuring on the inside to get hoses passed through a small hole without ripping insulation from them, leveling and allowing enough room at top to drop down in place. We were working with 10" ceiling. But, are very happy with results. Home Depot Workers could install this unit.

                    by|May 5, 2023

                      A:  Usually but you would need to call your local Home Depot for more information.

                      by|May 5, 2023
                        caret
                        Q:What is the minimum operating temperature that this unit will operate to in the winter
                        by|Apr 20, 2018
                        7 Answers
                        Answer This Question

                        A:  The minimum outside air intake in the heating mode is 4°F. Furthermore, the unit will start loosing its efficiency around 15°F.

                        by|Aug 30, 2019
                          1 found this answer helpful

                          A:  While there is no minimum a heat pump will reach a point where it is no longer effective. You can expect fairly good operation down to about freezing 32 F while in the twenties it will probably run continuously and the air coming out will not be very warm but will still "take the chill off". Once the outside temp is in the teens don't expect much at all. I would suggest that if you have a number of days below freezing that you have some kind of backup heating. I'm in Arizona and it hardly ever drops into the 30's. In the normal 40 degree winter temps the unit works great.

                          by|Jul 25, 2021
                            2 found this answer helpful

                            A:  Once below freezing efficiency drops very quickly.

                            by|May 29, 2020
                              2 found this answer helpful

                              A:  If it get's below zero it will not heat. It seems to stop around +3 degrees.

                              by|Aug 30, 2019
                                1 found this answer helpful

                                A:  The minimum outside air intake in the heating mode is 4°F / -20°C. Although the unit will start loosing its efficiency around 15°F

                                by|Aug 26, 2020
                                  4 found this answer helpful

                                  A:  Probably 60 degrees. That's pretty much the minimum for all A.C. units

                                  by|Jul 25, 2021
                                    1 found this answer helpful

                                    A:  I would not expect the unit to perform very well once the outside temperature drops below freezing. I have found that upper thirties and low forties the output into the room is still above eighty degrees. Like any heat pump, if you constantly have exterior temperatures below freezing, don't expect too much without back up strip heaters.

                                    by|Jul 25, 2021
                                      2 found this answer helpful
                                      caret
                                      Q:how many air handlers will this unit support
                                      by|Mar 26, 2018
                                      5 Answers
                                      Answer This Question

                                      A:  Only 1 air handler,has only port on condenser,

                                      by|May 5, 2023

                                        A:  It comes with unit that blows out the air. The white square box is the handler. This box mount to the wall. It like the units in a Motel.

                                        by|May 5, 2023

                                          A:  Only one air handler will this unit support.

                                          by|May 5, 2023

                                            A:  It is designed for one inside unit as far as I can tell.

                                            by|May 5, 2023

                                              A:  This particular unit is a single zone system that will support just one inside unit. The duel zone will have units will one outdoor unit and can support two indoor heads.

                                              by|May 5, 2023
                                                1 found this answer helpful
                                                caret
                                                Q:Is the 2 wire low voltage pre wired in this unit?
                                                by|Dec 22, 2017
                                                3 Answers
                                                Answer This Question

                                                A:  You must connect four wires at both ends.

                                                by|May 5, 2023

                                                  A:  No, the wire is supplied but you must connect both ends. There are four wires, two for the 120 volts supplied to the indoor unit from the outside unit and a ground wire and a signal wire. Diagrams in the booklet make this very easy.

                                                  by|May 5, 2023

                                                    A:  Dear Ryan Given the different configurations available the low voltage wire is not pre wired, but is easily installed. Thank you

                                                    by|May 5, 2023
                                                      caret
                                                      Q:How many wires are in low voltage wire?
                                                      by|Dec 21, 2017
                                                      2 Answers
                                                      Answer This Question

                                                      A:  4 in the one wire set and 2 in the other wire set.

                                                      by|May 5, 2023

                                                        A:  Four. Two to bring 120 volts to the inside unit to run the fan blower etc. one green ground and one to return control information to the outside unit. A 25 foot four wire cord is provided.

                                                        by|May 5, 2023

                                                          Frequently Bought Together

                                                          +
                                                          +
                                                          Price:
                                                          $1782.43

                                                          Compare Similar Items

                                                          current item

                                                          BTU Cooling Rating

                                                          24000 BTU

                                                          24000 BTU

                                                          24000 BTU

                                                          27000 BTU

                                                          Zone Capacity

                                                          1 Zone

                                                          1 Zone

                                                          1 Zone

                                                          2 Zone

                                                          Voltage (v)

                                                          220v

                                                          230/208v

                                                          220v

                                                          230v

                                                          BTU Heat Rating

                                                          24000 BTU

                                                          24000 BTU

                                                          24000 BTU

                                                          28000 BTU

                                                          Number of Tons

                                                          2 ton

                                                          2 ton

                                                          2 ton

                                                          2.25 ton