Questions & Answers

43Questions
caret
Q:The house is has aluminum wiring through most of it. I know arcs are a major issue with aluminum wiring. It would be very helpful to be ble to install these in key locations.
by|Jun 11, 2018
5 Answers
Answer This Question

A:  Yes, however it is recommended that you preform the standard aluminum to copper upgrade at all the termination points first. Google for additional details.

by|Dec 14, 2020
    8 found this answer helpful

    A:  Only CO/ALR rated devices can be direct connected with aluminum wire and these devices are not CO/ALR rated.

    by|Feb 16, 2021
    9 found this answer helpful

    A:  Hi Thank you for choosing Leviton. No, it's rated for copper or copper clad wiring only.

    by|Jan 31, 2021
      8 found this answer helpful

      A:  that depends on the rating. if they are approved for use with aluminum wiring.

      by|Feb 16, 2021
        5 found this answer helpful

        A:  I don't believe that Leviton model AGTR1 (arc fault/ground fault combo receptacle) is rated for use with aluminum wiring. You may need to pigtail the aluminum with copper or copper-clad wiring. If you go this route, the receptacle needs to be installed as the first outlet on the branch circuit in order to provide downstream protection. You also don't necessarily need GFCI protection for dry locations. My recommendation for aluminum wiring would be to replace the breakers in the panel with arc fault breakers. Home Depot carries a good variety of Eaton and Square D brand AFCI breakers.

        by|Jan 31, 2021
          8 found this answer helpful
          caret
          Q:Does the AFCI/GFCI come in light almond?
          by|Jun 2, 2018
          4 Answers
          Answer This Question

          A:  I think it does but not sure.

          by|Dec 14, 2020
            6 found this answer helpful

            A:  Hi , Thank you for choosing Leviton. Yes the catalog number is AGTR1-T.

            by|Jan 31, 2021
              7 found this answer helpful

              A:  Yes, this device comes in Light Almond, but my experience is that most who buy Light Almond later return them because they don't match their ivory devices.

              by|Feb 16, 2021
              9 found this answer helpful

              A:  Yes.

              by|Dec 14, 2020
                6 found this answer helpful
                caret
                Q:Could a AFCI/GFCI outlet like this be used so that a line voltage power cord could be run inside a wall cavity connected to a wall mounted TV?
                by|Feb 11, 2018
                3 Answers
                Answer This Question

                A:  Power cords are not permitted to be run inside a wall cavity.

                by|Feb 16, 2021
                9 found this answer helpful

                A:  No exactly sure of what you are doing. but the NEC does not allow a cord to be run inside wall or through a building structure. An extension cord cannot be used as a substitute for permanent wiring.

                by|Jan 31, 2021
                7 found this answer helpful

                A:  Flexible power cords like those used to connect TV sets are not approved as permanent wiring and there fore not allowed to be installed inside wall cavities or run through walls or floors. It has nothing to do with the protection on the wiring.

                by|Jan 31, 2021
                  7 found this answer helpful
                  caret
                  Q:Is it normal for these outlets to make a constant buzzing sound when powered up? I've tried multi...
                  by|Oct 15, 2017
                  1 Answer
                  Answer This Question

                  A:  Due to the circuitry inside, it's not uncommon for a GFCI/AFCI device to produce some electrical noise, but it's not something explicitly audible, unless one was to put their ear directly to the device.

                  by|May 5, 2023
                    caret
                    Q:does this meet the NEC 2014 requires for _Combination_ AFCI? (no, not the 'dual function' regarding the additional of GFCI. I realize it has GFCI built in as well). I ask because there are two types of AFCI protection- the 'older' regular AFCI, and the 'combination' AFCI, which detects more types of arcs. CAFCI is now required, and i can't tell if this covers the newer requirements like the dual function (C)AFCI-GFCI breakers do.
                    by|Jul 5, 2017
                    6 Answers
                    Answer This Question

                    A:  Yes it does. See packaging spec's. for confirmation.

                    by|Dec 14, 2020
                      6 found this answer helpful

                      A:  That is a good question. I do not have the answer to that. You would have to read the paperwork that comes with it. again good question.

                      by|Feb 16, 2021

                        A:  Yes, this device provides combination AFCI protection (both series and parallel).

                        by|Feb 16, 2021
                        9 found this answer helpful

                        A:  Yes, all Leviton AFCIs are combination-type, which means the unit can detect both series and parallel arcing.

                        by|Jan 31, 2021
                          9 found this answer helpful

                          A:  Yes. It is Series and Parrallel.

                          by|Dec 14, 2020
                            6 found this answer helpful

                            A:  They have been combination required (Series/Parallel Downstream, Upstream Series) for a while now, so new Leviton things like this are fully compliant with 2014/17

                            by|Feb 16, 2021
                            5 found this answer helpful
                            caret
                            Q:Will these fit in an older 1960's single metal box
                            by|May 20, 2017
                            7 Answers
                            Answer This Question

                            A:  Those boxes were pretty small so it would be a tight fit, but should fit if no more than 4 conductors are in the box. This would be a good application for a Dual Function AFCI/GFCI circuit breaker.

                            by|Feb 16, 2021
                            8 found this answer helpful

                            A:  Tight fit

                            by|Dec 23, 2020
                              6 found this answer helpful

                              A:  If you are asking about a standard metal outlet box, then it will fit unless there are a number of connectors in the box. If you are asking about a handy box, it may be too crowded. You can install a new box, right next to the breaker panel if you want, install this device in that box and connect the existing outlet circuit to this device. Then all outlets on the circuit will be protected.

                              by|Dec 23, 2020
                                9 found this answer helpful

                                A:  Probably, if you have line wires coming in and 2 load wires going out, you will have no wire nuts to connect, saving space. Wrap screws in electrical tape to eliminate shorting.

                                by|Jan 29, 2021

                                  A:  Without knowing the dimensions of the box it's hard to say, but older boxes are generally shallower than more current designs. I would think the new slimmer GFCI should fit, but if there are a number of additional wires in the box, it could be difficult.

                                  by|Dec 23, 2020
                                    6 found this answer helpful

                                    A:  maybe not in some but will in others of those years for sure.

                                    by|Dec 23, 2020
                                      6 found this answer helpful

                                      A:  Barely, but will fit. But, it also depends on how many wires, clamps in the box, and the cubic inch capacity of the box. There are lots of different size metal boxes, and NEC rules as to fill capacity.

                                      by|Dec 23, 2020
                                      6 found this answer helpful
                                      caret
                                      Q:Does this AFCI protect against both parallel AND series faults (as required by most recent NEC)?
                                      by|Apr 6, 2017
                                      1 Answer
                                      Answer This Question

                                      A:  Yes, this device provides serial and parallel protection to all downstream equipment, as well as serial protection upstream.

                                      by|May 4, 2023
                                        caret
                                        Q:To be used as sole AFCI protection for a circuit, the NEC (2017) requires four conditions be met: (1) Branch circuit wiring is continuous from the branch circuit overcurrent device (OCP) to the device (2) Maximum length of 14 AWG conductors between OCP and device is 50 feet. For 12 AWG wire, max is 75 feet. (3) The first outlet box (where this device is installed) must be marked (so future electricians know) and (4) "The combination of the branch-circuit overcurrent device and outlet branch-circuit AFCI shall be identified as meeting the requirements for a system combination-type AFCI and shall be listed as such." What breakers are listed with this device to provide the protection?
                                        by|Mar 3, 2017
                                        6 Answers
                                        Answer This Question

                                        A:  My question cites the NEC 2017. It was not eliminated from the code. UL has often stressed there were no breaker-device combinations listed as of last September. Leviton should address this.

                                        by|Feb 16, 2021

                                          A:  As far as I'm aware, UL has yet to develop/release the standard to which manufacturers can submit their products to be tested against.

                                          by|Jan 31, 2021
                                            7 found this answer helpful

                                            A:  No special breaker is required to be matched to an ARCI receptacle to comply with the code. Any standard breaker will suffice.

                                            by|Jan 31, 2021
                                              7 found this answer helpful

                                              A:  The protection designation is intrinsic to the design spec's of the receptical itself. A standard breaker, therefore, is the answer when theses requirements are to be met.

                                              by|Dec 14, 2020
                                                6 found this answer helpful

                                                A:  Any manufacturer's standard single pole 15 or 20 amp breaker is fine. It's interesting to note that the NEC referenced AFCI receptacles several years before any manufacturer even had them developed and on the market.

                                                by|Feb 16, 2021
                                                9 found this answer helpful

                                                A:  #4 That is in the process of going away, I don't know if they have issued the update, but it is out of the 2017 NEC. There is no " ULlisted" System combination circuit breaker. So use any branch circuit breaker. Most AHJ will allow you to use the 2017 NEC, even if your state has not adopted it, like CA.

                                                by|Dec 14, 2020
                                                6 found this answer helpful
                                                caret
                                                Q:Does this need to be connected to a combination afci/gfci breaker? or can it go to a standard breaker?
                                                by|Feb 24, 2017
                                                6 Answers
                                                Answer This Question

                                                A:  If you have a Dual Function AFCI/GFCI circuit breaker you don't need this device. This device should be connected to a standard single pole breaker.

                                                by|Feb 16, 2021
                                                9 found this answer helpful

                                                A:  Connect to any circuit protection device, breaker or fuse, and it will do its job.

                                                by|Feb 27, 2021
                                                  6 found this answer helpful

                                                  A:  This device acts as an AFCI/GFCI so it does not need to be put on a breaker that already provides that protection, though it certainly can be.

                                                  by|Jan 31, 2021
                                                    10 found this answer helpful

                                                    A:  Any standard breaker will suffice. No special breaker is required to meet code.

                                                    by|Jan 31, 2021
                                                    7 found this answer helpful

                                                    A:  This can be used as stand-alone or feed thru, and the overcurrent device can be a standard breaker. The NEC states where the device is placed in an individual circuit, under different circumstances. However, It can be used as a direct replacement for an existing GFCI or regular receptacle.

                                                    by|Dec 14, 2020
                                                    7 found this answer helpful

                                                    A:  Standard breaker.

                                                    by|Dec 14, 2020
                                                      8 found this answer helpful
                                                      caret
                                                      Q:I have been looking online and have not found a good answer. What is the correct way to wire th...
                                                      by|Nov 27, 2016
                                                      2 Answers
                                                      Answer This Question

                                                      A:  That is the correct way to wire it, breaker to AFCI/GFCI units in 1st outlet box. Can't use 3 wire (shared neutral) off of the AFCI/GFCIs to load receptacles. 2 wire to each receptacle, if splitting the receptacle both of the connecting bridges need to be removed.

                                                      by|May 4, 2023

                                                        A:  Backwiring the device will allow you to easily wire additional circuits off the Line or Load terminals, depending on which downstream circuits require protection. For wiring assistance, please call Leviton Tech Support at 1-800-824-3005

                                                        by|May 4, 2023

                                                          Frequently Bought Together

                                                          +
                                                          +
                                                          Price:
                                                          $3210

                                                          Compare Similar Protection Devices

                                                          current product
                                                          15 Amp 125-Volt Duplex Self-Test SmartlockPro Tamper Resistant AFCI/GFCI Dual Function Outlet, White
                                                          15 Amp Tamper Resistant AFCI Outlet, White (2-Pack)Decora Plus 15 Amp Industrial Grade Self Grounding Duplex Surge Outlet with Audible Alarm, White15 Amp 125-Volt Self-Test Tamper Resistant GFCI Outlet, White (4-Pack)
                                                          BrandLevitonLevitonLevitonLeviton
                                                          Name15 Amp 125-Volt Duplex Self-Test SmartlockPro Tamper Resistant AFCI/GFCI Dual Function Outlet, White15 Amp Tamper Resistant AFCI Outlet, White (2-Pack)Decora Plus 15 Amp Industrial Grade Self Grounding Duplex Surge Outlet with Audible Alarm, White15 Amp 125-Volt Self-Test Tamper Resistant GFCI Outlet, White (4-Pack)
                                                          Price
                                                          $3210
                                                          $3636
                                                          $3645
                                                          $5956
                                                          Ratings
                                                          (226)
                                                          (159)
                                                          (3)
                                                          (201)
                                                          Outlet TypeAFCI, GFCIAFCISurge ProtectionGFCI
                                                          Package Quantity1214
                                                          Indoor/OutdoorIndoorIndoorIndoorIndoor
                                                          DurabilityTamper ResistantTamper Resistant, Weather ResistantNot ApplicableTamper Resistant
                                                          Number of Outlets2222
                                                          Electrical FeaturesIndicator LightNo Additional FeaturesIndicator LightNo Additional Features
                                                          ConfigurationStandardStandardStandardStandard
                                                          GroundingGroundedGroundedGroundedGrounded
                                                          Voltage (V)125 V125 V125 V125 V
                                                          Outlet MaterialPlasticThermoplasticThermoplasticNylon
                                                          View ProductView ProductView ProductView Product