Questions & Answers

8Questions
caret
Q:Do I need a separate electrical panel for this unit or can it run off 110 breaker?
by|Aug 22, 2024
1 Answer
Answer This Question

A:  Hi Joseph and thank you for your question. Power Cord The electric power supply requirement for this water heater is 120 VAC/60 Hz, 2 amps. A dedicated circuit is recommended for the water heater. DO NOT connect to a GFCI or AFCI circuit. Multiple units may be connected to a single circuit up to the circuit rating. DO NOT use 3-prong to 2-prong adapters. DO NOT use power strips or multiple outlet adapters. All direct-vent gas models come with a 3-prong power cord. Only use this power cord and a matching grounded electrical outlet. All outdoor gas models DO NOT come with a power cord. Only hard-wire to an appropriate power outlet with a ground terminal. Keep any excess length of the power supply cord on the outside of the water heater. If local codes require hard-wiring, see instructions for “Hard-Wiring the Electrical Connections” below. Hard-Wiring the Electrical Connections Wiring should be performed by a qualified electrician in accordance with local codes. The water heater requires a properly grounded 120 VAC/60 Hz dedicated power supply. Multiple water heaters may be connected to a single circuit up to that circuit’s rating. DO NOT connect grounding wire to water pipes, gas pipes, telephone cables, lighting conductor circuits, or to any other grounding circuits that require a GFCI or AFCI (arc fault circuit interrupter). An ON/OFF switch must be provided and installed for the incoming 120 VAC power supply. Wire the water heater exactly as shown in the wiring diagram. This wiring diagram can also be found inside the water heater cover panel. The green screw is provided in the enclosure for a grounding connection. Connect the live wire to the black wire and neutral wire to the white neutral wire.

by|Aug 23, 2024
    caret
    Q:Can this unit be installed with an existing oil burner? Can any tankless be installed with an existing oil burner in single family home?
    by|May 25, 2024
    1 Answer
    Answer This Question

    A:  Hi Gdrums and thank you for your question. No it can not.

    by|May 28, 2024
      caret
      Q:Can the Rheem remote control Model# RTG20006DW be used with this heater?
      by|Feb 23, 2024
      1 Answer
      Answer This Question

      A:  Hi Stephen and thank you for your question. Yes it can.

      by|Feb 26, 2024
        caret
        Q:What is the minimum water pressure for this heater?
        by|Jan 2, 2024
        1 Answer
        Answer This Question

        A:  Hi Dave and thank you for your question. It is 14 psi.

        by|Jan 3, 2024
          caret
          Q:Currently I have a liquid propane hot water heater. It has a motor on top to vent vertically out of the basement. Does this unit require a motor for vertical venting?
          by|Oct 9, 2022
          1 Answer
          Answer This Question

          A:  Hi Meme and thank you for your question. No it does not.

          by|Oct 12, 2022
            1 found this answer helpful
            caret
            Q:Will this system work in conjunction with an exterior wood boiler?
            by|Sep 12, 2022
            1 Answer
            Answer This Question

            A:  Hi Brian and thank you for your question. The unit will function as a water heater as long as you meet the requirements/minimums: 1 - minimum flow rate of .40 2 - minimum temperature rise of 35 3 - exceed the unit's 5gpm@25' head 4 - the temperature coming into the unit must not go over 120F. 5 - the water to the unit must me potable with no added chemicals.

            by|Feb 17, 2023
              1 found this answer helpful
              caret
              Q:I have two 40 gallon water heaters in my home does that mean I need two tankless water heaters
              by|Aug 16, 2021
              2 Answers
              Answer This Question

              A:  It depends on your incoming water temp and overall usage expected. Ours runs multiple showers/sinks at once, that our previous (single) 40gallon tank would not have been able to do

              by|Jan 20, 2022

                A:  Hi ron alarid and thank you for your question. It may not. You would want to call 866-720-2076 for assistance with sizing the unit(s).

                by|Aug 17, 2021
                  caret
                  Q:Can Pex tubing be used for the condesate drain? Also, if the remote is connected, can the water temp also be controlled at the unit?
                  by|Jun 23, 2018
                  1 Answer
                  Answer This Question

                  A:  No, As per the Use & Care manual only PVC , CPVC pipe or flexible tube can be used for the condensate drain line.

                  by|May 5, 2023