Questions and Answers for Southwire 500 ft. 4/0-4/0-4/0-2/0 Gray Stranded AL SER Cable

Internet #202316402

Model #13107801

Store SKU #412502

  • For use in almost all applications where type SE cable is allowed
  • For wet or dry locations up to 90˚C or 194˚F
  • 600-volt maximum

Questions & Answers

42Questions
caret
Q:Is this wire good for mobile home feeder
by|Feb 3, 2016
2 Answers
Answer This Question

A:  SER cable cannot be used underground at all; not direct buried and not in conduit.

by|Jun 4, 2021
8 found this answer helpful

A:  The answer to your question is: no. Mobile Home Feeder is a direct burial rated wire and SER is not. We would suggest ordering our actual Mobile Home Feeder cable (4/0-4/0-4/0-2/0 AL MHF model # 28714401). The above advice is based upon the current edition of the National Electric Code (NEC). Free access to the latest version of the NEC is available online at www.nfpa.org/freeaccess. The NEC and local building codes regulate the types of wire and cable that can be used in specific electrical applications, as well as the manner of installation. Check your local building codes before you start any wiring and cable electrical project and be sure to obtain required permits. When your work is complete, always have it inspected for compliance with local codes to ensure that it has been safely installed.

by|Oct 3, 2020
    6 found this answer helpful
    caret
    Q:What size conduit does this require?
    by|Jan 14, 2016
    2 Answers
    Answer This Question

    A:  SER cable isn't required to be in conduit in a typical residential installation between the 200A service disconnect and 200A service panel (subpanel).

    by|Jun 4, 2021
    8 found this answer helpful

    A:  I am using 3 inch conduit.

    by|Jun 4, 2021
      caret
      Q:do you need to run the wire in conduit from the main panal to a sub panal in an out building
      by|Dec 20, 2015
      2 Answers
      Answer This Question

      A:  SER cable cannot be used underground at all; not direct buried and not in conduit.

      by|Mar 16, 2022
      9 found this answer helpful

      A:  As building codes differ from city to city, we suggest that you check with your local building inspector.

      by|Jun 4, 2021
        1 found this answer helpful
        caret
        Q:I am adding an RV power outlet box (100 amp) to my workshop. What aluminum wire would would be correct for a 20' run from my 200 amp panel indoors run through wall studs and going through to outside wall of a covered carport to mount the box. Box has breakers for a 50 amp plug, 30 amp plug, and a 20 amp gfci outlet. I will only be using the 50 and 20 concurrently. 30 amp plug will only be used if needed by a visitor.
        by|Nov 19, 2015
        2 Answers
        Answer This Question

        A:  Call an electrician.

        by|Apr 25, 2023

          A:  I would use aluminum 2-2-2-4 SER cable. No conduit required, but it must be secured to framing.

          by|Jun 4, 2021
          8 found this answer helpful
          caret
          Q:Installing 100 amp sub panel in basement. Wire run 55-60 feet. Above ground. Thru framing and crawl space. Main panel is 200 amp.
          by|Oct 6, 2015
          2 Answers
          Answer This Question

          A:  This cable would be fine for your application, but technically should be protected by a 90 amp breaker.

          by|Jun 4, 2021
          8 found this answer helpful

          A:  Yes. That is rated for 100 amp

          by|Mar 7, 2021
          5 found this answer helpful
          caret
          Q:I need to install a service wire in the attic from my 400 Amp panel to my new 200 Sub Panel. It is a total distance of 70 feet, maybe 65 Feet, considering a voltage drop of 3% & I dont want to use conduit so it would probaly have to be SER Aluminum. What size wire and does Home Depot sell it by the foot? Or would it be less expensive to run 2" conduit loose Copperor Alumuim from Panel to Panel. My labor is free so dont use time as a factor.
          by|Sep 12, 2015
          3 Answers
          Answer This Question

          A:  The “dwelling” ampacities given on the SE cable datasheet (see below) assumes that the product is used as a residential service conductor rather than as a feeder. When used as a feeder, 4/0-4/0-4/0-2/0 SER cable has an allowable ampacity of 180 Amps (not 200 Amps) as long as it isn’t installed in thermal insulation. If it is installed in thermal insulation, the ampacity is further reduced to 150 Amps [per NEC 338.10(B)(4)(a)]. 4/0-4/0-4/0-2/0 SER cable is not large enough for your application. http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet273 The rest of this discussion assumes that you are not installing the cable in thermal insulation. Furthermore, you will need to reduce the ampacity of the cable due to the higher ambient temperature in the attic. For example - if the max ambient temperature in your attic is between 122°F and 131°F, per the NEC the allowable ampacity of a 250 kcmil AL conductor will be 175 Amps. The largest over-current device (OCD) you could use with the cable in this situation is 175 Amps, not 200 Amps. If the max ambient temperature in your attic is between 113°F and 123°F, per the NEC the allowable ampacity of a 250 kcmil AL conductor will be 189 Amps. In this situation, you can use the round-up rule to use this cable with a 200 Amp OCD. The bottom line is that if your maximum ambient temperature in the attic is 122°F or less, you can use 250-250-250-3/0 AL SER cable. Your voltage drop will be less than 3% for a 70’ run when using 250 AL SER. When using SER as interior wiring, insure that you comply with NEC Article 338 for Service Entrance Cable. There are specific requirements for the installation methods you can use. You can access the NEC for free at www.nfpa.org/freeaccess. It is likely less expensive to install AL SER cable rather than single conductor building wire and conduit, even if you don’t include the labor cost. If the above explanation didn’t make sense to you, you are strongly advised to hire a licensed electrician that understands this situation.

          by|Oct 6, 2021
            9 found this answer helpful

            A:  This is the correct cable for your application and yes, HD sells it by the foot.

            by|Jun 4, 2021
            9 found this answer helpful

            A:  4/0 Ser is definitely a better alternative. It is usually sold by the foot but check with your local store

            by|Oct 3, 2020
            5 found this answer helpful
            caret
            Q:Can this SER cable be direct buried underground?
            by|Sep 12, 2015
            2 Answers
            Answer This Question

            A:  SER cable cannot be used underground at all; not direct buried and not in conduit.

            by|Oct 30, 2019
            1 found this answer helpful

            A:  This product is not rated for direct burial.

            by|Oct 30, 2019
              3 found this answer helpful
              caret
              Q:IS THIS UNDERGROUND SERVICE?
              by|Aug 30, 2015
              3 Answers
              Answer This Question

              A:  Yes

              by|May 15, 2021

                A:  SER cable cannot be used underground at all; not direct buried and not in conduit.

                by|May 15, 2021
                3 found this answer helpful

                A:  No, this wire is not recommended for direct burial.

                by|Aug 31, 2020
                  4 found this answer helpful
                  caret
                  Q:Does this cable meet this requirement? "Type USE (Underground Service Entrance) conductors are not permitted to enter a building unless they are also identified with the additional markings RHH and RHW (triple-rated)."
                  by|Aug 3, 2015
                  2 Answers
                  Answer This Question

                  A:  Answer: Yes, Type SER cable can be used inside a residence and in fact one of its primary functions is wiring from the meter base to the distribution panel. Type SER cable can be used out doors in above ground applications only. You can get spec sheets at Southwire.com under the product catalog page.

                  by|Oct 30, 2019
                    3 found this answer helpful

                    A:  This cable meets your requirement ONLY if you have a disconnect at your meter and your main panel is a subpanel.

                    by|Oct 30, 2019
                    1 found this answer helpful
                    caret
                    Q:I'm planning to use this cable from my new 200 Amp Main Service Breaker to a 200 Amp Distribution Panel located in the garage. The length of cable will be approximately 50 feet. The cable will be routed vertically within the stud walls, and horizontally thru the loft / attic space. Do I need to run this cable within a conduit?
                    by|Jul 26, 2015
                    4 Answers
                    Answer This Question

                    A:  This cable does not need to be run in conduit. However by code you cannot pull a 200 service off of existing 200 amp service unless it is a disconnect. 100 amp would be the largest you could pull. And it will also depend on your current load. If you have electric as a primary heat source you may be even more limited. Contact a qualified electrician or your local building department.

                    by|Jun 7, 2021
                    3 found this answer helpful

                    A:  This cable does not need to be installed in conduit unless additional protection is required.

                    by|Jun 4, 2021
                    7 found this answer helpful

                    A:  No conduit needed. But you will have to sheetrock any stud bay up to 8' to protect the wire.

                    by|Jun 4, 2021
                    5 found this answer helpful

                    A:  Hi RonP, you are going to have to contact your local building department to ensure you get the correct codes for your city.

                    by|Apr 27, 2023
                    4 found this answer helpful

                    Frequently Bought Together

                    +
                    +
                    Price:
                    $4849.03

                    Compare Similar Items

                    current item

                    Conductor Material

                    Aluminum

                    Aluminum

                    Copper

                    Cable/Wire Type

                    SER

                    URD

                    SER

                    Max Amps

                    200

                    315

                    200

                    Total Wire Length (ft.)

                    500 ft

                    500 ft

                    500 ft

                    Features

                    Heat Resistant, Jacketed, Waterproof

                    Heat Resistant, Jacketed, Waterproof

                    Heat Resistant, Jacketed, Waterproof