Q:Can this load center be installed upside down With the main breaker on the bottom indoors?
by|Jan 30, 2024
1 Answer
Answer This Question
A: Bobs,
Yes, The NEMA 1(indoor) CONVERTIBLE Mains, can be bottom fed by rotating the complete load center and cover. This will NOT cause the labeling to be "upside down", it will just start the circuit counting at the bottom of the cover where the Mains is located, but it will read appropriately.
https://www.se.com/us/en/faqs/FA121184/
Warm regards. Schneider Electric Customer Care
by|Feb 23, 2024
1 found this answer helpful
Q:Do Eaton BR breakers fit in the Homeline 200 Amp 30-Space 60-Circuit Indoor Main Breaker Plug-On Neutral Load Center with Cover(HOM3060M200PCVP) box?
by|Jan 23, 2024
1 Answer
Answer This Question
A: Patrick,
Unfortunately No. Each manufacturer has it's own UL listings for their specific products based on their specific product line and their specific combination of products.
Warm regards. Schneider Electric Customer Care
by|Jan 23, 2024
Q:What do 80 circuit mean for 40 spaces
by|Jan 22, 2024
1 Answer
Answer This Question
A: Hi,
It means that the every space on the load center can be used with tandem breakers, evey single pole tandem come with 2 circuits, so if you install 40 tandems you can have 40x2=80 circuits.
Warm regards. Schneider Electric Customer Care
by|Jan 23, 2024
Q:I have a box up in my block wall garage. I don't want a mess of ugly wires coming down the wall ,&,, into my breaker box. So have you ever, heard the wires are going to get to hot this way and start a fire,?? Please look at Pic Ty.
by|Jan 17, 2024
1 Answer
Answer This Question
A: Hi,
In order to help you we need to know more information about your application with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter.
Warm regards. Schneider Electric Customer Care
by|Jan 22, 2024
Q:I purchased this panel and it seems to missing one of the yellow covers for the hot lines into the main breaker. I received 2 covers but they are both the same and the best I can tell there should be different ones for each side of the breaker.
by|Dec 3, 2023
1 Answer
Answer This Question
A: Hello LSH1,
We apologize for any inconvenience you might have encountered with our products. Let me assure you that our products are continually being improved based on user feedback. In order to help you we need to know more information about your experience with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter.
Warm regards. Schneider Electric Customer Care
by|Dec 5, 2023
Q:I see the panel is breaker fed but does it how straight to the breaker or does it hit lugs? Or can you remove the breaker and make it straight lug fed?
by|Dec 3, 2023
1 Answer
Answer This Question
A: Hello Charles,
Yes, the HOM3060M150PCVP is a convertible load center, it can be converted to main lug.
You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter.
Warm regards. Schneider Electric Customer Care
by|Dec 5, 2023
Q:Since this is a plug-on neutral, load center why do you provide old style, non-plug-on neutral breakers with it? That makes no sense.
by|Nov 27, 2023
2 Answers
Answer This Question
A: Real answer: New breakers are much more expensive and they want to seem like they are "giving" you a deal with their "value pack". In reality, they are getting rid of their old stock.
by|Mar 6, 2024
A: Hello RPDD,
The standard full size Homeline branch breakers can be used in the new Homeline plug-on neutral (PoN) load centers. This would include the old style GFI, AFI, and CAFI breakers with the white neutral pigtail wire (the pigtail wire on these breakers would still be wired to the neutral bar).
Regards, Schneider Electric Customer Care
by|Dec 8, 2023
Q:What is the bus bar rateingon the 100a ?
by|Nov 16, 2023
1 Answer
Answer This Question
A: Hi,
The bus bar rating on the HOM2448M100PCVP is 125A.
Warm regards. Schneider Electric Customer Care
by|Nov 20, 2023
Q:I will be using 500kcmil to serve this panel, will it fit in the main lugs? If not how would I adapt the wire size?
by|Nov 16, 2023
1 Answer
Answer This Question
A: Hi,
Unfortunately this device only accepts up to 250 kcmil wiht the main breaker, even with the lugs installed instead of the main breaker accepts up to 300 kcmil, In order to help you we need to know more information about your application with this product. You can contact us anytime using our chat live https://www.se.com/us/en/work/support/customer-care/contact-schneider-electric.jsp where an agent will be able to give you further assistance on this matter.
Warm regards. Schneider Electric Customer Care
by|Nov 16, 2023
Q:3 questions on the 150 amp 30 space 60 circuit panel: 1) Does this come with the 150 amp main breaker? 2) What is the wire range for the main & neutral lugs? 3) is there a lug adapter that can be put on the ground bar to accept larger gauge wire?
by|Nov 13, 2023
1 Answer
Answer This Question
A: Hello JDM1,
1) the HOM3060M150PCVP load center comes with a 150A main breaker factory installed.
2) the wire range (AWG/kcmil) for the main and neutral lugs is 4–250 Au/Cu
3) unfortunately, there is no lug adapter for the ground bar to accept a larger gauge wire.
Regards, Schneider Electric Customer Care