Questions and Answers for GE PowerMark Plus Outdoor 70 Amp 2-Space 4-Circuit Single-Phase Main Lug Circuit Breaker Panel

Internet #100201548

Model #TL270RCUP

Store SKU #598650

  • Outdoor NEMA 3R enclosure
  • Main lugs are factory installed
  • Use with equipment ground kit TGK4 (order separately)

Questions & Answers

76Questions
caret
Q:In the description it says "top or bottom feed" Can the internal buss bar be flipped to put the Lugs at the bottom instead of at the top ? I need to replace my defective existing panel, but the existing feed wires will not reach the lugs when they are located at the top of the buss bar. Thanks
by|Jun 16, 2021
2 Answers
Answer This Question

A:  'Top or bottom' continued..... After studying the pictures and descriptions , I do think it would be very easy to flip the buss assembly, *** However it would be very, very difficult to get the dead front to fit the circuit breakers decently. Guess I will need to get a few split bolts and a few feet wire, to extend the feed wires coming from the bottom so they reach the lugs, at the top of the panel. ( Use split bolts to splice the wires if you do not have a large crimper. )

by|Mar 22, 2023
    1 found this answer helpful

    A:  So after studying this panel it is not possible to flip the bus bar assembly, I must extend my existing bottom feed wires to reach the lugs at the top. Home Depot does have some set screw type wire couplings that should work to add the extra needed wire length, at a reasonable price.

    by|Jun 17, 2021
      caret
      Q:I want to replace a defective existing panel. As a 'Main Lug panel', can I flip the internal bus bar assembly to be a bottom feed ? Thanks
      by|Jun 16, 2021
      0 Answer
      Answer This Question
      caret
      Q:As a Main Lug panel, can the interior 'guts' be 'flipped' for a bottom feed ? I am replacing an existing panel and the existing incoming wires are too short to reach the top of the buss bar. Thanks !
      by|Jun 16, 2021
      3 Answers
      Answer This Question

      A:  You would have to attach at least four clips with tapped holes for the panel screws. I recommend using In-Line Splice Kits to extend the wires instead to avoid voiding the UL on the panel.

      by|Jun 16, 2021

        A:  Reply to Sparky : Thank you for your response. This is being used as a 100 amp sub-panel with a 100 amp breaker feeding from the Main Service Entrance. However the original installer used 3/0 copper, which is more than a little "over-sized" ! That is hard enough to bend normally, but when you add a splice, crimped or set screw type, it locks the strands from flexing, there by making the 3/0 copper even harder to bend. My current tool inventory only includes a crimper that goes up to number one AWG. Then add enough tape for a safe long term splice, there will be some large 'eggs' on these conductors. So while "splicing/extending" is one option, I would like to avoid that, if possible.

        by|Mar 6, 2023

          A:  So... Turning the buss assembly top lugs down looks relatively simple, HOWEVER the dead front breaker cover would NOT ever fit proper ! *** NO CHOICE but to extend my existing bottom feed wires.

          by|Jun 17, 2021
            caret
            Q:I need to install a main breaker in this panel. What is the item number for the 200A main beaker?
            by|Jun 9, 2021
            1 Answer
            Answer This Question

            A:  There is no item number for a "200" amp breaker in a "125" amp panel! The most you can put is a 125 amp breaker.

            by|May 29, 2024
              2 found this answer helpful
              caret
              Q:How many knockouts are in this box?
              by|May 11, 2021
              0 Answer
              Answer This Question
              caret
              Q:What size wire do I run from main panel to 70 amp sub panel
              by|Jan 19, 2021
              2 Answers
              Answer This Question

              A:  Thank you for your question. The size wire depends on many factors, the length of the run, wire type, etc.

              by|Mar 29, 2021

                A:  I would encourage you to look up an ampacity chart readily available online to confirm your individual situation. If using romex or UF cable #4 would carry 70 amps under normal conditions. The temperature and length of run may change that so please confer with a qualified electrician or professional engineer to confirm. Thanks for the question.

                by|Jun 4, 2021
                  2 found this answer helpful
                  caret
                  Q:Can I use a 40 amp 2-pole breaker (240 v) in this panel?
                  by|Sep 22, 2020
                  1 Answer
                  Answer This Question

                  A:  Thank you for your question. Yes, the TL270RCUP will accept 2pole 40a breakers THQL2140 or THQP240.

                  by|Sep 22, 2020
                    caret
                    Q:I've got one of these small sub panels and thought I had some bad breakers. As it turns out the bars that the breakers connect to (circled in red) have failed- they aren't hot any longer. This seems like an odd failure after 8 years....am I wrong?
                    by|Sep 5, 2020
                    2 Answers
                    Answer This Question

                    A:  This is not a sub-panel, It is a Disconnect box for that purpose only. Used in HVAC mostly. Once is awhile they fail. ! out of 10,000.

                    by|Feb 19, 2021

                    A:  Make sure that you add di-electric grease to the lugs, wire ends, and breaker contacts. It can be messy and the reasons to do so are not obvious until you get to a corrosion failure. The grease is available at home depot, but you may have to ask for help. I have had quite a few breakers and a several panels fail in San Francisco where the long term effects of being near the ocean accelerates the corrosion on outdoor panels that are miles from the ocean. Use the grease to prevent this long term problem.

                    by|Nov 13, 2020
                      caret
                      Q:Where can i order the 125 amp main breaker?
                      by|Jul 28, 2020
                      0 Answer
                      Answer This Question
                      caret
                      Q:what is the wire range for the Main Lugs supplied?
                      by|Jun 26, 2020
                      1 Answer
                      Answer This Question

                      A:  Thank you for your question. The TL270RCUP main lugs accept #6 to #3 AWG wire.

                      by|Jul 6, 2020

                        Frequently Bought Together

                        +
                        +
                        Price:
                        $43.89

                        Compare Similar Items

                        current item

                        Number of Circuits

                        4

                        4

                        4

                        1

                        Maximum Amperage (A)

                        70

                        70 A

                        70 A

                        100 A

                        Indoor/Outdoor

                        Outdoor

                        Indoor

                        Outdoor

                        Outdoor

                        Breaker Box Type

                        Subpanel

                        Subpanel

                        Subpanel

                        Main Breaker Panel

                        Mounting Type

                        Surface

                        Flush

                        Surface

                        Surface